Author Topic: TA-10 burning up Kelmar CO dousers
Ken Layton
Phenomenal Film Handler

Posts: 1452
From: Olympia, Wash. USA
Registered: Sep 1999


 - posted 10-01-2001 08:48 AM      Profile for Ken Layton   Email Ken Layton   Send New Private Message       Edit/Delete Post 
Sounds like the description of a "snubber" circuit.

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 10-01-2001 01:55 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Gordon, thank you for the information.

Paul

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 10-01-2001 09:27 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
It is a snubber but I have never had the thing short unike a lot of standalone ones

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 10-01-2001 10:18 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Gordon, since we are working with inductive reactance, I would presume the capacitor value might be critical. What would your recommendation be on capacitance and what size resistor would you recommend?

Paul


 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 10-02-2001 07:48 AM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
If memory serves it is around .1UF 5,000vpiv and a 22 ohm resistor

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 10-04-2001 01:19 AM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Got my coil in, and replaced it. Just to be sure it was not a stuck relay that caused it, I swapped a few around.

I'll let you know if it fries again.

Paul

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 11-24-2001 05:12 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Brad, I should have taken your advice about adding a fuse in the CO circuit, or Gordon's recommendation about using a 100-watt light bulb. The same automation, in the same house, fried another CO open coil.

Any other suggestions?

Paul


 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 12-03-2001 12:27 AM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Well, this weekend, I had a bad start on my 4:00 run. I forgot to turn on the platter take-up. When I started the show, naturally the TA-10 shut the system down. (great - just as advertized).

However, when I rolled up the film spewed on the floor, I attempted to re-start, followed by an immediate shutdown again. Once more a re-start, motor restarted ok, the film motion and film presence led's were lit on the fail-safe, but one film status LED's was "off" (I honestly can't remember which one it was...) on the automation. (no reason whatsoever.) Then, No. 3 shut down when the lamp in no. 2 finally fired, and the LED on the film status lit.. When #3 was restarted, the lamp on No. 2 went out, and it would not come on until I manually over-road it at the automation. The motor was running on automation, but the sound format had to also be manally over-ridden. At the end of the show, I brought it down manually, except for the motor. On film tail-out, the alarm went off again, and the motor shut down just like it was supposed to.

Did Bill Gates write the program?

I think two things happened here which was intially caused by my screw-up of not turning on the take-up motor.

1. The automation froze in the middle of the cycle. (This would account for the possibility of frying another CO Open coil.
2. The automations are talking to each other through space or the power lines. (they are not connected via any interlock circuit whatsoever). Seems kind of odd when one Xenon lamp fires, it shuts down another projection station without sounding an alarm.

Nice, huh? <I wander off talking to myself...> Hmmmm. I think I have a grounding problem.

Back again....Oh, by the way - I am using switcher power supplies for the Xenon lamps. Strong International type, driving 3000w lamps.

Anyway, now this is what I call "Bad Start".

Paul


 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 12-05-2001 01:25 AM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Just an update.

It was reported to me today that the TA-10's in the two houses had a great day talking to each other, and shutting each other down like cats and mice. Starting up #2 would shut down #3. Then when #3 was re-started, it shut down #2. After trying to re-start #2, it again shut down #3. The projectionist got so frustrated she rebooted the whole damn thing, from the ground up. She finally got both No. 2 and 3 running.

So I went to the theater, pulled the covers off the power panels, and made a very careful inspection. I noted that the electricians forgot to pull a separate ground into the power panels, and the entire projection stations were basically "floating". Apparently there may be a loose compression fitting somewhere in the EMT maze in the ceilings and rafters which might be preventing a good ground to the projection station raceways, pull boxes, flex EMT, xenon power supplies, pedistals, etc.

I took a No. 8AWG wire and bonded the neutral to the ground, as the neutral was grounded anyway in the main distribution panel.

Then it occured to me that it may not have been the automations causing all this trouble. It may have been lamp ignition emitting a high level of RF (which they certainly do). The poorly grounded projection stations acted like huge antennas. I have a tendency to believe this RF was getting into the automation's CPU, and driving it nuts. I can also see that it might be possible for a CPU to get so confused that it closed the CO Open relay and fried its coil, just like these damned PC's and their "Illegal Functions and will now self-distruct, Press any key to continue".

So far, so good. There were no additional reports that came to me today saying that more shutdowns have occurred.

I think I found the trouble.

Time will tell.

Paul


 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 12-05-2001 08:07 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
Paul,

Please tell me you are going to go back and pull in the proper ground wires rather than leave the current neutral-ground thing.

Certainly the grounding issue must be resolved to clear the problem and while experimenting, anything goes but neutral/=ground except right after the step down transformer...hence on the first panel after the transformer, the Neutral buss and ground buss may be the same. It is also an indication that the panel is the first in the line of any further subpanels.

Once proper grounds are pulled in, noise supression will be significantly better for everything concerned, including sound and your rectifier's diodes. I, not too long ago, had a theatre where the diodes were failing at an amazing rate and they weren't overheated...come to find that the lamphouses had such a good paint job, the ground was compromised and that the caps in and around the igniter had nowhere to drain to...after using star washers on the lamphouses to ensure good ground to the chassis, problems vanished overnight.

Steve

------------------
"Old projectionists never die, they just changeover!"

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 12-05-2001 09:26 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
Also it is worth noting that under the NEC all raceways (because they are painted) and flex must actually have a ground wire bonding them to the emt or even better to the panel

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 12-05-2001 09:55 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Steve, you absolutely correct. The electrical contractor who wired that building is going to be saddled with that responsibility very soon, probably within the next day or so.

I was reluctant to even experiment with this thing. But one thing I can say - it is a new building, and the electrical contractor is the one who is going to get that building up to code. I don't know how it slid by the electrical inspector in the first place. It is a major job, and I don't have the equipment to perform such an operation.

Also, it is uncertain what was done in other sub-panels. As it stands right now, if we dump the main neutral and have a major load imbalance, all or very much of the EMT could come "hot"!

Gordon, you are also correct. Ground wires are pulled trhough the flex now. It used to be that if it was less than 5 feet, it did not need a separate ground.

Now, the real task is going to be getting all the hoop jumping, feet kissing, and finger pointing behind us so that this job can be finished correctly.

(and you know how that goes..)


 |  IP: Logged

Oscar Neundorfer
Master Film Handler

Posts: 275
From: Senoia, GA
Registered: May 2000


 - posted 12-06-2001 07:14 AM      Profile for Oscar Neundorfer   Author's Homepage   Email Oscar Neundorfer   Send New Private Message       Edit/Delete Post 
I am usually cloistered in my lab and do not get into the field nearly as much as the rest of you guys do, but what little I manage to get out there, I have seen horrendous wiring problems concerning grounding. Improper power distribution, especially in the grounding, can cause more wierd and apparently unsolvable problems than you can imagine. I have heard from too many people that even when the wiring is properly specified in the blueprints, that far too many electrical contrators simply ignore the plans and do it their way because they "know better". Add to that poorly done wiring plans, and you have a recipe for a nightmare.

In these days when so much of the electronics is microprocessor based, and when there are far more sources of EMI/RFI and all kinds of nasty spikes, harmonics due to computer switching supplies, etc. on the AC lines, it is absolutely imperative to have the best possible wiring and grounding done. Electricians need far more training on the problems and solutions regarding sensitive electronic equipment. Contractors need to learn to do things the right way and not "their" way. Building owners/cinema corporate people need to hold the electrical contractors' feet to the fire and not let them get away with ANYTHING wrong. There is just too much expensive and sensitive equipment in projection booths to settle for anything less than a first class power distribution system. I believe this will correct many of today's problems.

------------------
Oscar Neundorfer
Chief Engineer
SMART Devices, Inc.

oscar@smartdev.com

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 12-09-2001 07:29 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
This sounds almost like a weekly update.

For the most part, the grounding did take care of the problem. But one more problem popped up. Manual shutdown or fault shutdown on one machine took out one of the other machines, too.

After banging my head on the wall, I looked up and saw that a strange pipe was also coming out of the speaker wire pull boxes on the wall. All of the speaker wire pull boxes were connected together.

Hmmmmmm....Seems as though the installer used the speaker wire pull boxes as a non-sync feed from the other projection stations. Also, I noticed a Beldon 8451 cable interfacing all of these pull boxes. I followed the wires out, and those wires went into the automation. After yanking the covers off the TA-10's, the 8451 was connected to the "Data port" terminals.....

Since we don't and never will use this option, I disconnected all of those wires to the data port terminals on all automations.

Between the grounding problems and this data port thing, it has been a rollercoaster ride to find out what the hell was wrong.

Things seem to be running normally now, except for the igniter in No. 2 sometimes does not ignite, and the motor on No. 3 takes to long to build up to speed. Film Motion Fault shuts it down. But these two problems have also been with us since day one, so those are different problems to solve in the near future. There are lots of other minor problems that have to be addressed, such as movable masking that doesn't want to move, some more platter motors that are in poor shape, mis-cut aperatures, things like that.....

I am beginning to think this was a bad installation.

I am glad I had nothing to do with it.

Paul


 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 12-15-2001 03:24 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Update: The disconnection of the Data Port terminals corrected the problem of the TA-10's talking to each other and driving everyone nuts.

I still wonder why the data port cables were pulled through the speaker wire raceways......Arg! I would never do that.....

I also removed the bonds between the neutral and grounds that I installed in the power sub-panels. But we are still waiting for an electrician to get us up to snuff.


 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.