Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-02-2002 03:41 AM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
Hi Pat,

In addition to answering my queries in regards to timed cues above, it seems there is a flaw in your advice via the "sync loop 0 / sync on" mode.

First show of the day...all works perfect.

Second show of the day...all works perfect, BUT the status panels never say when the film has stopped. The green run light just stays lit even after the show is over. Upon inspecting the projector, the projector and lamphouse have done a normal shutdown, but the automation says "RUNNING" and has "cue 4" displayed where there is no such things as cue 3.

Here is the show programming:
CUE 0 - SR / MID1
CUE 1 - DIGITAL / DOWN
CUE 2 - DIGITAL / MID2
CUE 3 - NON-SYNC / UP / SHOW END

Any ideas? The only way to clear it so that another show can be ran is to press STOP then CUE INPUT.


 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-03-2002 02:53 PM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
*bump*

 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-04-2002 01:56 PM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
Ummmm, there has to be SOMEONE that works for Eprad or Strong that can address this quirk with the CNA-150.

 |  IP: Logged

Ken Lackner
Phenomenal Film Handler

Posts: 1907
From: Atlanta, GA, USA
Registered: Sep 2001


 - posted 09-04-2002 03:43 PM      Profile for Ken Lackner   Email Ken Lackner   Send New Private Message       Edit/Delete Post 
Brad: When in Sync Mode, if you are actually syncing and the sync loop is not 0, I believe all the units will say "running" until the last one in the chain reads the shutdown cue. I know you are not actually syncing here, but what happens when the last show of the day drops? Then do they all go back to 0? My guess is that they would.

 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-04-2002 07:11 PM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
What you say makes perfect sense, but I wouldn't know as just like
any booth when the movies start to drop for the night, the operator starts
powering each unit down.  By the way, I am running in sync loop "0".


Pat?  Rick?  Brian?  Hello? 


 |  IP: Logged

Ken Lackner
Phenomenal Film Handler

Posts: 1907
From: Atlanta, GA, USA
Registered: Sep 2001


 - posted 09-04-2002 07:58 PM      Profile for Ken Lackner   Email Ken Lackner   Send New Private Message       Edit/Delete Post 
So next time you close, perform an experiment. Leave them all on until the last one drops. Or do the test with a few trailer packs running on, say, 3 or 4 machines. (Not that any of this will solve your problem. I'm just very curious. )

 |  IP: Logged

Rick Sanjurjo
Film Handler

Posts: 26
From: Omaha, NE, USA
Registered: Jul 2002


 - posted 09-06-2002 07:54 AM      Profile for Rick Sanjurjo   Email Rick Sanjurjo   Send New Private Message       Edit/Delete Post 
Brad,

I have tried and two other people have tried running programs, both in sync loop 0 and on other sync loop numbers and have not had any problems as long as there have been no other units on the same sync loop number. The problem maybe a bug in an older software revesion, could you tell me what version software is running.

Rick

 |  IP: Logged

Alan Gilbertson
Expert Film Handler

Posts: 148
From: Carpentersville Il 60110
Registered: Nov 1999


 - posted 09-06-2002 01:16 PM      Profile for Alan Gilbertson   Author's Homepage   Email Alan Gilbertson   Send New Private Message       Edit/Delete Post 
Jay or Tom at Eprad I'm sure can give you the answer or answers right away.
(419)666-3266

 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-07-2002 04:22 AM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
quote:
" I know you are not actually syncing here, but what happens when the last show of the day drops? Then do they all go back to 0? My guess is that they would."

You are indeed correct Ken. I had the booth intentionally left powered on and nothing touched for the final round and as soon as the last projector dropped, all of them stopped "running".

I am going to go through all of the units tomorrow and make sure they are assigned properly. I forgot to get the software version off of them today. I'll do that tomorrow.


 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-08-2002 02:06 PM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
Ok, all of the units are ID'd properly and the software is revision 3.050

Help, please, someone?


 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-10-2002 03:53 AM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
Well guessey what started today. One of the automations (in the big house of course) started spazzing out and decided to stop a show randomly during the feature! Yes indeedy, there's nothing like renting out an auditorium for an important screening and the damned automation stops the projector THREE TIMES in the middle of the movie!!! Rather than quoting what was said, let's just say this did not make people happy and I have them running that screen completely manual now.

But that's not all, now another unit is randomly missing cues as of yesterday.

Pat, Rick, whoever...something has got to be done as this theater has had constant problems ever since it opened. In speaking to the manager and projectionist that has been there from the opening, not one day has gone by where all of the automations have worked properly. These are only 1 year old. What is this saying about the product??? Is this just a bad batch of lemons and the rest of the CNA line of automations are reliable, or does this sort of nonsense happen with all of these automations? Help me out here. This needs to be remedied, and after what happened tonight, this needs to be remedied immediately. What can and will Strong do to back their product and fix this situation?


 |  IP: Logged

Jean-Michel Grin
Expert Film Handler

Posts: 222
From: Geneva & Lausanne, Switzerland
Registered: Jul 2002


 - posted 09-10-2002 04:48 AM      Profile for Jean-Michel Grin   Author's Homepage   Email Jean-Michel Grin   Send New Private Message       Edit/Delete Post 
Brad,

I experienced the same problem with two projectors in Interlock mode. One of the CPA-10 stopped 3 time the show during the feature
I'm disapointed of theses automation from Strong for theses sporadic malfunction.
In hope that you can find a solution

Good luck !

sincerly yours,

------------------
Jean-Michel Grin - Europlex Cinemas (Switzerland)

 |  IP: Logged

Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 09-10-2002 05:00 AM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
Hey, I'll go in there and pull the interlock wires if Strong thinks that will fix the problem. Overall I just have not been impressed with the CNA-150s due to their lack of programmability, non-user friendly layout, no fader control, no start cue circuit that works reliably, no programmable delay lines, and now sporadic random stopping in mid-performance. Plus, I have yet to receive resolving support from Strong on these issues and the projectors never stop "running" when the show is over.

If these issues cannot be addressed and resolved within a reasonable time frame, I am ready to throw in the towel on the CNA line of automations, get the money refunded and buy CA-21s. The CA-21s will do everything this theater needs with reliability, and if needed, support from Pennywise.


 |  IP: Logged

Rick Sanjurjo
Film Handler

Posts: 26
From: Omaha, NE, USA
Registered: Jul 2002


 - posted 09-10-2002 01:19 PM      Profile for Rick Sanjurjo   Email Rick Sanjurjo   Send New Private Message       Edit/Delete Post 
Brad,

The problems you describe are consistent with having multiple units on the same sync ID number or having the sync wires reversed or not properly terminated somewhere in the loop. The sync number issue is not only on the automations but also on the status boxes. All items connected to the loop have to have different syn ID numbers. You can trouble shoot it by disconnecting the units from the sync lines and seeing if the problems goes away, if so you have identified the problem. The current version of software is 3.080 and that might explain why we can’t recreate your starting in interlock problem at the office, the dealer you bought the automations from should be able to get you the upgrade on the software. Your interlock problems could also be related to the sync wiring or ID issue.

As far as timers and cue wait instruction goes, someone didn’t purchase the correct automation for their application. The CNA-200 is what you need to get the features you require, the CNA-150 is a lower cost unit and was not designed to give the functionality you are looking for, a little bit of research or a phone call before the purchase of the units would have been prudent.

Hope I have helped

Rick

 |  IP: Logged

Sean McKinnon
Phenomenal Film Handler

Posts: 1712
From: Peabody Massachusetts
Registered: Sep 2000


 - posted 09-11-2002 11:44 PM      Profile for Sean McKinnon   Author's Homepage   Email Sean McKinnon   Send New Private Message       Edit/Delete Post 
Brad if it stays "Waiting for cue 4" can't you just add another cue after your normal shutdown cue?

------------------
--Sean McKinnon
Manager
Loews Cineplex Entertainment
Freshpond Mall 10
Cambridge, Mass
<A HREF="http://www.enjoytheshow.com" TARGET=_blank>www.enjoytheshow.com</A>

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 4 pages: 1  2  3  4 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.