 - posted 01-03-2003 09:13 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
I doubt that you will find any closed delta power being used in new construction these days. It is all open delta as some have pointed out.

I think you will also find the reason for the electrical contractor's request is to make sure the load is balanced, and that you have adequate ampacity in the facility's wiring.

 |  IP: Logged

John Walsh
Film God

Posts: 2490
From: Connecticut, USA, Earth, Milky Way
Registered: Oct 1999


 - posted 01-03-2003 10:52 PM      Profile for John Walsh   Email John Walsh   Send New Private Message       Edit/Delete Post 
At our recently-opened theater in Minneapolis, we specified all audio equipment be on the same phase, and lighting be on the same phase. This was documented in the drawings, and the architect just made every breaker panel the same for every auditorium.

The electrical inspector noted this, and insisted we "break up" the load arrangement because (he said, giving an example) if all the lights are on the same phase at all panels, the phases may be unbalanced.

So, we had to change which phase things went on at each auditorium. Luckly, this theater had 15 auditoriums, so five panels had one arrangment, (lights on phase A for example) the next five a different arrangement (phase B) and the last five on phase C.

I wanted to simply switch around the three power leads inside the breaker box, so the breakers would be in the same location for every auditorium, but on differnt phases. (I really like making all equipment the same since it's easier to train people.) The electrical inspector could not think of anything in the code that would'nt allow this, but "just didn't like the idea" so would not allow it.

Since we use projectors with freq converters, the issue of phase matching for interlocking projector motors wasn't a concern.

Does anyone think this is a bad idea?

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 01-03-2003 11:03 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
In a building in canada all panels are supposed to have the phases in the panel the same
I usually buld the audio racks for a 60amp single phase feeder with a breaker on each outlet down the strip inside the rack this ensures the rack is treated as a single device (they also get approved in my shop as such)

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 01-03-2003 11:06 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
The only thing I can see that would be an issue is phase rotation. But, since there are no phase sensitive equipment present, who cares?

However, if you have a 3 phase motor or a HVAC 3 phase system, I can see why the electrical inspector would not allow it.

It could be he didn't allow it because of the "standardization issue".

 |  IP: Logged

Jack Ondracek
Film God

Posts: 2348
From: Port Orchard, WA, USA
Registered: Oct 2002


 - posted 01-04-2003 11:46 AM      Profile for Jack Ondracek   Author's Homepage   Email Jack Ondracek   Send New Private Message       Edit/Delete Post 
quote:
from Paul T:
And be advised....if any of this equipment does not have a UL certification... be prepared to spend alot of time finding out the UL info the contractor/inspector wants.

You still whining about that relay, Paul? [Big Grin]

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 01-04-2003 02:28 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Jack, you darn tootin! [Big Grin]

But actually, I thought that would be a good thing to post, as there are many others who fall into that trap. [Smile]

 |  IP: Logged

Bruce Hansen
Jedi Master Film Handler

Posts: 847
From: Stone Mountain, GA, USA
Registered: Dec 1999


 - posted 01-04-2003 06:57 PM      Profile for Bruce Hansen   Email Bruce Hansen   Send New Private Message       Edit/Delete Post 
The three phases should be balanced, that is, have the same amount of current draw. If the phases are not balanced you will have a high neutral current. This will result in a voltage on the neutral, and this is one of the causes of hum in audio, and video. I recently received a phone call from a friend who had just had a video facilty wired all on the same phase, because that is how he was told to advoid hum. He had terrible hum problems. I told him to forget what he had been told, and rewire things to balance the phases. The hum went away.

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 01-04-2003 07:12 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
In a properly grounded sound system the influence of neutral current is a non issue. Also proper sizing of the neutral conductor is criticle
Several new studios actualy use a balanced neutral where neutral is actually 60v out of phase with the hot legs

 |  IP: Logged

Adam Fraser
Master Film Handler

Posts: 499
From: Houghton Lake, MI, USA
Registered: Dec 2001


 - posted 01-04-2003 10:34 PM      Profile for Adam Fraser   Author's Homepage   Email Adam Fraser   Send New Private Message       Edit/Delete Post 
We have the 480v 3 phase and there are three or so transformers outside the building for us. And to put things into perspective we have a 12 ft by 12 ft room in the basement completely dedicated to power boxes and knife switches. Altough this might be overkill for a 1 screen, it sure makes it easy to troubleshoot when we have power problems. I second the lightning rods though, we got hit by lightning a couple years back and it somehow knocked out our 3 phase power, left our single phase alone, and finally grounded out through our well pump.

 |  IP: Logged

Bruce Hansen
Jedi Master Film Handler

Posts: 847
From: Stone Mountain, GA, USA
Registered: Dec 1999


 - posted 01-05-2003 05:50 PM      Profile for Bruce Hansen   Email Bruce Hansen   Send New Private Message       Edit/Delete Post 
With all due respect, Gordon, you may have something confused. If a conductor has 60 volts on it, it is not a neutral; the three phases are out of phase with each other, so how would you phase the neutral you are talking about? I can't see how that would ever work, and it would NEVER NEVER NEVER pass electrical code here in the states. What you may be thinking about is: sending the three phases to a group of outlets, but only one neutral, and connecting all the neutrals on the outlets to this one neutral. If the current flows of the three phases are balanced (the same) there will not be any neutral currnet traveling back to the bracker box, and no voltage drop across the neutral run back back to the bracker box. This concept has been used here for a long time to keep hum down, especialy for long power runs.

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 01-05-2003 06:36 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
Sorry but that is what I ment it is gaing popularity in some US westcoast studios and has gained alot of popularity up here in broadcast studios

 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 01-05-2003 09:21 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
What it is termed here in the states is "Balanced Power" There are special restrictions on its use and installation with proper notifications.

All legs are "hot" and its chief purpose is noise immunity.

You'd be surprised what will fly here in the states. I don't recall any of the conductors being termed "Neutral" though. Neutral carries a specific meaning and MUST always be coded White for 120VAC service or Grey in 277 (in the US).

Steve

 |  IP: Logged

Richard Fowler
Film God

Posts: 2392
From: Ft. Lauderdale, FL, USA
Registered: Jun 2001


 - posted 01-05-2003 09:58 PM      Profile for Richard Fowler   Email Richard Fowler   Send New Private Message       Edit/Delete Post 
Hmmm......grounding to the rebar on the roof of a building in Mexico....running to ground and neutral buss bars in different locations of a booth in Peru.....Exposed ballast resistors glowing on a wall in Brazil....40 HZ and below power in India....we need more pilots [Frown]

 |  IP: Logged

Jeffry L. Johnson
Jedi Master Film Handler

Posts: 809
From: Cleveland, Ohio, USA
Registered: Apr 2000


 - posted 01-06-2003 02:04 PM      Profile for Jeffry L. Johnson   Author's Homepage   Email Jeffry L. Johnson   Send New Private Message       Edit/Delete Post 
Balanced Power
Equi=Tech
Equi=Tech Balanced Power FAQ

How does balanced power help to solve ground loop humming
here
The Origin of Balanced Power
here

 |  IP: Logged

John Hawkinson
Film God

Posts: 2273
From: Cambridge, MA, USA
Registered: Feb 2002


 - posted 01-07-2003 01:17 PM      Profile for John Hawkinson   Email John Hawkinson   Send New Private Message       Edit/Delete Post 
Huh. This is all interesting and fascinatingly disturbing stuff.
Jeff's last link asserts this is referenced in Article 530(G) of the 1996 NEC. In case anyone was wondering, I decided to go dig around in the NEC to see what it says.

It turns out that it's not in 530 anymore in the 2002 NEC, but there are some references elsewhere. (Article 530 is "Motion Picture and Television Studios and Similar Locations").

Instead, balanced power seems to be the subject of Article 647, "Sensitive Electronic Equipment." They seem to refer to it both as "sensitive electronic equipment" as well as "Technical Equipment," though the term "technical equipment" seems to be used elsewhere within the NEC(*).

I suppose the only terribly interesting comments in the NEC are in Section 647.7 Receptacles, (A) General:
code:
(1) All 15- and 20-ampere receptacles shall be GFCI pro-
tected.
(2) All outlet strips, adapters, receptacle covers, and face-
plates shall be marked with the following words or
equivalent:
WARNING--TECNICAL POWER
Do not connect to lighting equipment.
For electronic equipment use only.
60/120 V. 1{phi}ac
GFCI protected
(3) A 125-volt, single-phase, 15- or 20-ampere-reated recep-
tacle outlet having one of its current-carrying poles
connected to a grounded circuit conductor shall be lo-
cated within 1.8m (6 ft) of all permanently installed
15- or 20-ampere-rated 60/120-volt technical power-
system receptacles.
(4) All 125-volt receptacles used for 60/120-volt technical
power shall have a unique configuration and be identi-
fied for use with this class of system. All 125-volt,
single-phase, 15- aor 20-ampere-rated receptacle outlets
and attachment plugs that are identified for use with
grounded circuit conductors shall be permitted in ma-
chine rooms, control rooms, equipment rooms, equip-
ment racks, and other similar locations that are re-
stricted to use by qualified personnel

(*) For what it's worth, the only way I see to get to Article 647 from Article 530 is a reference in 530.11 "Permanent Wiring" permitting "communication circuits; audio signal processing, amplicfications, and reproduction circuits; Class 1, Class 2, and Class 3 remote-control or signaling circuits and power-limited fire alarm circuits shall be premitted to be wired in accordance with Articles 640, 725, 760, 800." Why is this relevent/interesting? Well, mostly it's not, but Article 640 ("Audio Signal Processing, Amlification, and Reproduction Equipment" defines "Technical Power System" as "An electrical distribution system with grounding in accordance with 250.146(D), where the equipment grounding conductor is isolated from the premises grounded conductor except at a single grounded termination point within a branch-circuit panelboard, at the originaging (main breaker) branch-circuit panelboard, or at the premises grounding electrode." Maybe I'm reading that wrong, but that seems to imply to be incompatible with the idea of "technical power" meaning 60V/120V balanced power. (250.146(D) permits isolated receptacle grounds not tied to the closest panelboard but instead terminating at some central grounding location)

In an additional bit of irony, other parts of Article 640 refer to balanced power as "a seperately derived system with 60 volts to ground" (640.7(B) and 640.9(A)(2)).

Bleh. These NEC/NFPA people could really use a decent techwriter and copy editor. [Mad]

--jhawk

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 3 pages: 1  2  3 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.