» Film-Tech Forum ARCHIVE   » Operations   » Film Handlers' Forum   » CP650 rebooted mid-show for no particular reason, WTF? (Page 2)

 
This topic comprises 2 pages: 1  2 
 
Author Topic: CP650 rebooted mid-show for no particular reason, WTF?
Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 12-06-2008 01:15 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
Even if it is an electronic switch...you have the potential for failure...again...this was an APC unit...and one I see in a great many places...a 2U rackmount version (I don't have the VA size committed to memory) but it communicates serially, among other things and has a decent front panel display to show its status.

Relay or no, it didn't do so well on the handoff from line to battery...at least in some conditions. It was not intrinsic to the unit as the replacement had no problems and the several other units, also installed in 2003 have not had problems.

Steve

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 12-06-2008 01:26 PM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
quote: Steve Guttag
The better kind of UPS are the ones that generate their own sine-wave power and ALWAYS have the plugged in devices on UPS power. Think of the batteries as "buffers." They are always being filled while the unit is plugged in...if the power is lost, the batteries will then drain. However, the equipment that is plugged in is unaware of any power change. There is no transition time and the power is always clean.
There's another advantage to the latter, 'on-line' type of UPS, though it applies mainly to the larger sizes. They are available with a three phase rectifier and single phase inverter, so they can produce a single phase output for the equipment while presenting a balanced load to the supply. We installed a 16 kVA one this year with enough battery capacity for a one hour runtime at full load, though we can get longer as we have configured less important devices to shut down sooner. We are likely to install additional battery capacity in the not too distant future. This is the first UPS of this type that we have installed, and we have ben very pleased with it. I'm trying to get funding at the moment for another one, with lower power rating, but increased battery capacity for a much longer run time to support the telephone system

We really need UPSs at the moment; our supply is heavily overloaded, the Voltage is low, builders who are doing a total refurbishment of the building keep cutting the supply to things that they shouldn't, and the other day we were seeing funny Voltages in one part of the building, constantly changing, and anywhere from 160V - 296V, on different phases with about 55V from the blue phase to neutral. I actually had difficulty persuading them that we had a neutral floating and we really needed an electrician to look at it urgently.

 |  IP: Logged

Joe Redifer
You need a beating today

Posts: 12859
From: Denver, Colorado
Registered: May 99


 - posted 12-06-2008 07:42 PM      Profile for Joe Redifer   Author's Homepage   Email Joe Redifer   Send New Private Message       Edit/Delete Post 
What is the point of keeping the CP650 on a UPS if the projector cannot also remain running with full light output in addition to the powerful amplifiers with thousands of watts of sheer power? I have had power fluctuations and my CP650s did not reboot or even kick back into Non-Sync, but all of the xenons did shut off and automatically restrike.

 |  IP: Logged

Mike Blakesley
Film God

Posts: 12767
From: Forsyth, Montana
Registered: Jun 99


 - posted 12-06-2008 08:27 PM      Profile for Mike Blakesley   Author's Homepage   Email Mike Blakesley   Send New Private Message       Edit/Delete Post 
Because we have this crappy electrical system here in town that is prone to 2 or 3 second power outages during lightning storms. We can't afford to have a big enough backup power system to run the whole booth during these but at least we don't have to wait for the 650 to reboot.

I don't think the UPS was the cause of this problem though - we didn't have even a slight blip in the power that I noticed - and our other computers kept running fine.

 |  IP: Logged

Mark Gulbrandsen
Resident Trollmaster

Posts: 16657
From: Music City
Registered: Jun 99


 - posted 12-06-2008 11:13 PM      Profile for Mark Gulbrandsen   Email Mark Gulbrandsen   Send New Private Message       Edit/Delete Post 
I could also e-mail you the latest firmware version which is also very stable and you could upgrade it... its very easy... I can walk you through it over the phone... You just need a puter with a serial port, a straight through serial cable... the CP-650 Setup program and the firmware .bin to load in. The new version is also very stable...

Mark

 |  IP: Logged

Tony Bandiera Jr
Film God

Posts: 3067
From: Moreland Idaho
Registered: Apr 2004


 - posted 12-11-2008 05:44 PM      Profile for Tony Bandiera Jr   Email Tony Bandiera Jr   Send New Private Message       Edit/Delete Post 
quote: Joe Redifer
..What is the point of keeping the CP650 on a UPS if the projector cannot also remain running with full light output in addition to the powerful amplifiers with thousands of watts of sheer power?...
The point is to avoid the long reboot time, and also help reduce the chance of blowing any of the CP-650's circuits in the event of a spike / surge..

And Steve's experience puzzles me, as I have both CP's and AMX control systems on UPS and have NEVER had either act up on the transtion from utility to UPS and back.

And I'm using the APC's Back-UPS ES line (the cheapest ones they make.)

Only other thing I can think of causing those troubles is if a surge is getting in thru the "back door" by some other connected device. Of if the particular Crestron program requires communication from an outboard device, and when that comm is lost the Crestron reboots.

 |  IP: Logged

Mike Blakesley
Film God

Posts: 12767
From: Forsyth, Montana
Registered: Jun 99


 - posted 12-12-2008 09:47 AM      Profile for Mike Blakesley   Author's Homepage   Email Mike Blakesley   Send New Private Message       Edit/Delete Post 
Update: We got through the whole next week's 12 shows plus a pre-screening of our Polar Express matinee with no problems. We are opening Twilight tonight so if it happens again, it'll be tonight!

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.