Robert Minichino
Master Film Handler

Posts: 350
From: Haskell, NJ, USA
Registered: Dec 2005


 - posted 12-16-2009 04:42 PM      Profile for Robert Minichino   Author's Homepage   Email Robert Minichino   Send New Private Message       Edit/Delete Post 
Not in a corner-grounded delta [Big Grin]

 |  IP: Logged

Tim Reed
Better Projection Pays

Posts: 5246
From: Northampton, PA
Registered: Sep 1999


 - posted 12-16-2009 05:55 PM      Profile for Tim Reed   Author's Homepage     Send New Private Message       Edit/Delete Post 
quote: Randy Bowden
I think that goes without saying.
Then, why would anyone call a wild leg a hot leg? They're all hot. [Confused]

 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 12-16-2009 06:37 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
Around here, they are all called "high-leg" and yes, the abundance of every 3rd breaker not being filled is the give away. If the panel is open, you should have a Black, a Red and then either an Orange, Yellow or Brown on the "high-leg". If you work in an "old town" you are going to come across the high-leg situation.

I have also come across the grounded Delta...just plain freaky if you ask me, and I'm an EE. There is something un-nerving about seeing one of the phases tied to ground and that the remaining two hot legs having a 220 potential to ground. The reason I was given was that it reduced cost as only three conductors needed to be pulled of the heavy copper instead of four...and only double pole breakers instead of triple.

Since most don't get Delta power and also most will have 120V circuits in their system, a grounded Delta does not come up much...in fact, only once in my time in the booth (about 30-years).

High-leg has come up multiple times though...its more annoying than anything since you have to get a breaker panel that is 33% larger to get the breakers you need. In a couple of these situations, the building had high-leg for 3-phase only and had a separate service to the building for single phase power (120/240). I would prefer that if offered since there are generally 10-20 single phase circuits versus 3-phase. I suspect that ratio is going to go higher as we move to switch mode power supplies for the newer projectors since most DCinema projectors only need single phase up to 4KW.

Steve

 |  IP: Logged

John Hawkinson
Film God

Posts: 2273
From: Cambridge, MA, USA
Registered: Feb 2002


 - posted 12-16-2009 08:12 PM      Profile for John Hawkinson   Email John Hawkinson   Send New Private Message       Edit/Delete Post 
Remember, specific color codes aren't mandated NEC or most jurisdictions -- so don't count on any particular color meaning anything anywhere -- ever.

Steve, I've recently seen electricians install a split-phase panel (well, it was rated for 208 hot-to-hot) on a 3-phase system and only pull two of the phases to it. Their thinking was they believed the customer had specified a very large number of loads all to be on the same phase (...) and so most of the panel positions would have ended up empty if they'd used a 3-phase panel. Of course, guarantee of unbalanced loads.

But in a 3-phase high-leg scenario, where the unbalanced load is a given, that seems a reasonable way to go.

--jhawk

 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 12-16-2009 08:20 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
While it is true about the color code...the only protected color is WHITE for Neutral, I've generally found the color code pretty well respected...incuding in high-leg situations.

Now wires in a trough...no, I don't trust the jackets to mean anything...I presume all a lethal.

Steve

 |  IP: Logged

John Hawkinson
Film God

Posts: 2273
From: Cambridge, MA, USA
Registered: Feb 2002


 - posted 12-16-2009 09:16 PM      Profile for John Hawkinson   Email John Hawkinson   Send New Private Message       Edit/Delete Post 
I dunno, I hear green is pretty reliable too [Smile]

I have recently, canyoubelieveit, seen red for isolated ground (as distinct from the EGC which was green). Not real clear on how that could pass inspection.

--jhawk

 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 12-16-2009 09:40 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
Oddly enough Green is not a protected color...though, in my opinion, it should be. Personally, I think all of the standard colors should be codified and enforced at least for 120V and higher circuits.

Again, White is the only color that I'm aware as being protected as being a Neutral.

 |  IP: Logged

Jake Spell
Master Film Handler

Posts: 294
From: Johns Island SC
Registered: May 2009


 - posted 12-17-2009 02:36 AM      Profile for Jake Spell   Email Jake Spell   Send New Private Message       Edit/Delete Post 
Yes White is the only color that is protected, however I have seen White used as a ground. Dont know how this passed inspection, I also have see plenty of people using the ground as a nuetral when they have a 240 volt appliance, with a small 120 load (like a 120 light in an attic that uses one hot from the A/C and the ground) when the installer is to lavy/cheep to run a netural back to the pannel

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 12-17-2009 04:31 AM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
Jake: at one point all electric stoves were wired using the neutral as a ground. I wondered about this as a child. Now code requires 4 wires; seperate the ground from the neutral. Louis

 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 12-17-2009 06:35 AM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
Yeah, using ground as a current carrying conductor (neutral) is dangerous. It is also true that electrical wiring/codes have evolved as the flaws in original designs showed themselves. Shoot, my house only had 2-prong outlets until I changed them. You can kinda tell when the 120/240 outlet come into being considering that a 240 outlet is a 6-series and the 120/240 is a 14-series. The outlet we all know as a standard 120V is a 5-series.

Steve

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 12-17-2009 07:14 AM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
How common are those 240 V delta system sover there? I've only ever seen one, 120/208 and 277/480 Wye systems seem to be much more common, though I have to admit that I haven't seen many American installations. Whenever I'm in a building and see an electrician working I must admit that I have a look to see what sort of system it is.

We've got some horrible nonsense over here, caused by European harmonisation. Live wires used to be red, yellow and blue, with neutral black and earth green. Lives have now become brown, black and grey, yes seriously, with neutral blue and earth green with yellow stripe. So, blue, which used to be a phase conductor, is now neutral, and black, which used to be neutral, is now a phase conductor. Great opportunity for confusion when new wiring is added to an existing installation. The new neutral blue does seem to be a slightly lighter shade than the old blue. In mixed installations a special warning label has to be attached; I can't remember the exact wording.

'European harmonisation' was also the excuse, sorry reason, why all fire extinguishers now have to be red, rather than different colours for different types.

 |  IP: Logged

Eric Robinson
Jedi Master Film Handler

Posts: 538
From: Santa Rosa, CA
Registered: Jan 2005


 - posted 05-23-2010 09:10 PM      Profile for Eric Robinson   Email Eric Robinson   Send New Private Message       Edit/Delete Post 
This is also known as a "bitch leg" or "stinger leg"

Be careful when using this setup with a Strong console. The strong console "Highlight IIa" for instance takes the 3 phases and passes them to the xenon power supply. (no problem here)
However:
The console also takes each phase and divides the load so that one phase powers the projector motor, the next powers the automation and fans, the next the convenience outlets... so if you have a stinger leg, you could pass 220V to one of these 120V devices.

 |  IP: Logged

Steve Guttag
We forgot the crackers Gromit!!!

Posts: 12814
From: Annapolis, MD
Registered: Dec 1999


 - posted 05-23-2010 10:15 PM      Profile for Steve Guttag   Email Steve Guttag   Send New Private Message       Edit/Delete Post 
Eric,

Yes and no. There is a strap that is often installed so that the "C" phase powers the two 120V circuits. However, a competent installer will remove that strap and fire the the TWO 120V circuits from individual breakers. Or, failing that, use two legs of the 3-phase and rotate them about the complex to ensure the electrical panel load is balanced.

We service a former AMC house that used those stupid straps and they had the "C" phase severely overloaded as compared to the other two legs. It caused numerous 3-phase breaker failures since the C buss bar would get hot and transfer that heat to the three phase breakers.

That strap is a lazy person's way of installing...it is an incompetent way of installing a system.

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 05-24-2010 11:53 AM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
quote: Steve Guttag
I have also come across the grounded Delta...just plain freaky if you ask me, and I'm an EE. There is something un-nerving about seeing one of the phases tied to ground and that the remaining two hot legs having a 220 potential to ground. The reason I was given was that it reduced cost as only three conductors needed to be pulled of the heavy copper instead of four...and only double pole breakers instead of triple.
In some Parts of Europe, though not the UK, there are three phase electric railways that work this way, two of the phases are carried on twin overhead wires, with pickup via a split pantograph, and the third, grounded, phase is on the running rails. It's an obsolete system now, but still in use in some places; I think Italy has some of this.

The other place I've seen something similar, on a much smaller scale is on static single to three phase converters. The 240 V single phase supply is stepped up to 415 V by an autotransformer, and the third phase is derived via a capacitor network and the inductance of the motor windings. I don't like these things; any given model will only work over quite a limited range of load, no neutral is available for use with the three phase output, and two of the phases are at 415 V from ground, rather than 240 V as in our normal 415 V three phase.

 |  IP: Logged

Robert Koch
Film Handler

Posts: 93
From: Williams Ca USA
Registered: Apr 2006


 - posted 05-24-2010 02:06 PM      Profile for Robert Koch   Email Robert Koch   Send New Private Message       Edit/Delete Post 
At my advanced age, when we were young we always called it "the stinger".

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.