Steve Kraus
Film God

Posts: 4094
From: Chicago, IL, USA
Registered: May 2000


 - posted 04-19-2015 10:29 PM      Profile for Steve Kraus     Send New Private Message       Edit/Delete Post 
 -

I created this to use for a few days until a proper outlet was installed on a dailies job. This is just for the lamp rectifier.

Those are two ordinary 120V line cords. The pilot lights indicate power on each cord with the third indicating the cords were properly plugged into outlets on different phases (or opposite sides of the 120/240 source in a single phase situation). If plugged into the same phase, the two input pilots would light but not the third. The switch is double pole since there are two hots to be interrupted. It's a kludge to be sure but I tried to make it as safe as possible.

Something like this could work with a pair of long 120V extension cables (especially if you have to go a long way to find an outlet on a different phase) OR with the kludge box near the outlets and a long 208/240V extension (which you might make up yourself).

 |  IP: Logged

Richard Fowler
Film God

Posts: 2392
From: Ft. Lauderdale, FL, USA
Registered: Jun 2001


 - posted 04-20-2015 01:12 AM      Profile for Richard Fowler   Email Richard Fowler   Send New Private Message       Edit/Delete Post 
Your power supply requires 12 ampere at 220VAC to run reliably….so the step up transformer noted would not have enough power due to being limited by the input.
Steve's type of box is used in some video rental situations with professionals being cautious regarding usage. Long extension cord runs will have to be factored that there will be some line voltage drop.

 |  IP: Logged

Marcel Birgelen
Film God

Posts: 3357
From: Maastricht, Limburg, Netherlands
Registered: Feb 2012


 - posted 04-20-2015 02:43 AM      Profile for Marcel Birgelen   Email Marcel Birgelen   Send New Private Message       Edit/Delete Post 
quote: Brian Darwas
Mike, the machines can run on both 50hz and 60hz with different size pulleys. In The U.S. The pulleys are a bit smaller since the motor is running a bit faster.
I'm not sure if you were referring to me, but this answers my question anyway. [Wink]

quote: Richard Fowler
Steve's type of box is used in some video rental situations with professionals being cautious regarding usage. Long extension cord runs will have to be factored that there will be some line voltage drop.
I guess you put the box as close to your 110V sources as possible. With 220V, the loss is already better manageable if using a wire of sufficient gauge. But it would be interesting to know how long such an extension cord would need to be.

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 04-20-2015 06:51 AM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
Louisville area runs about 127 volts. Low of 123. Southern Indiana runs a low of 127 and a high of 135 (near generating plant.)

 |  IP: Logged

Scott Norwood
Film God

Posts: 8146
From: Boston, MA. USA (1774.21 miles northeast of Dallas)
Registered: Jun 99


 - posted 04-20-2015 08:23 AM      Profile for Scott Norwood   Author's Homepage   Email Scott Norwood   Send New Private Message       Edit/Delete Post 
135? Wow. I suppose that light bulbs don't last very long there, even if people in that area are using 130v bulbs.

 |  IP: Logged

Brian Darwas
Film Handler

Posts: 10
From: New York, NY
Registered: Nov 2014


 - posted 04-20-2015 10:36 AM      Profile for Brian Darwas   Email Brian Darwas   Send New Private Message       Edit/Delete Post 
- Marcel, I was referring to you. I was posting from my phone and my brain somehow read your name as Michael, my apologies.

- Steve Kraus, that box you built looks good, might be just what I need. The one thing I have to ask is how do you make the third light illuminate only when plugged into opposing phases of power?

Thanks.

 |  IP: Logged

Steve Kraus
Film God

Posts: 4094
From: Chicago, IL, USA
Registered: May 2000


 - posted 04-20-2015 01:55 PM      Profile for Steve Kraus     Send New Private Message       Edit/Delete Post 
The two basic indicators were connected across each input's hot and neutral. The third one is connected across the two input's hots. If you have both input indicators lit but not the third, your cords are both connected to the same phase. Move one.

Indicators like that are usually good for up to 240V but just to be safe I put two in series for the 208/240 indicator and left one inside the box.

Be aware that this is not to code and strange, potentially dangerous things can happen. If one input line is live, the switch is on, and the load (the lamphouse) is on, the other (unplugged) cord will have 120V present on its "hot" prong. That's dangerous.

If one line is live, and the other is plugged into an outlet whose breaker is off but has various other loads on the same circuit, your load may be exposed to 120V instead of 208/240 as the other loads on that circuit pass the current.

Used properly for a temporary situation, it's fine. I disclaim any responsibility! Get someone with electrical knowledge to build and advise.

 |  IP: Logged

Brian Darwas
Film Handler

Posts: 10
From: New York, NY
Registered: Nov 2014


 - posted 04-20-2015 02:31 PM      Profile for Brian Darwas   Email Brian Darwas   Send New Private Message       Edit/Delete Post 
Thanks Steve, I actually have two good friends that are licensed electricans. I'll run this idea by them and see what they say, or think about it. they might have some ideas of their own to add, or yell and tell me not to do it, lol.

Is it possible to have a fuse that trips both circuts if one circut loses power?

I know I'm dragging this out a bit, but some good "do's" and "don't's" have come up.

 |  IP: Logged

Marcel Birgelen
Film God

Posts: 3357
From: Maastricht, Limburg, Netherlands
Registered: Feb 2012


 - posted 04-20-2015 06:19 PM      Profile for Marcel Birgelen   Email Marcel Birgelen   Send New Private Message       Edit/Delete Post 
That's not really how a fuse works. [Wink]

You could probably come up with a circuit that cuts the other input and the output if not both inputs are present, but probably not something off the shelf.

quote: Louis Bornwasser
Louisville area runs about 127 volts. Low of 123. Southern Indiana runs a low of 127 and a high of 135 (near generating plant.)
I don't really understand why the voltage near a generating plant would be higher in a complex, synchronized grid. Isn't your local grid voltage more a thing of local regulation and practices of your utility, combined with the distance to the nearest transformer?

Also, a typical power plant has nowhere near 100% availability.

 |  IP: Logged

Brian Darwas
Film Handler

Posts: 10
From: New York, NY
Registered: Nov 2014


 - posted 04-20-2015 07:01 PM      Profile for Brian Darwas   Email Brian Darwas   Send New Private Message       Edit/Delete Post 
Sorry, shouldn't have said fuse, lol. A fuse would have to be overloaded, then burnt out.

Could I over do it and have two solenoids (or relays) that are powered from the opposite circut? This way if one circut loses power it automatically cuts the power to the other circut?

I'll probably just stick with keeping these indoors. Maybe I can find a 120v lamphouse. Everything else runs on 120v except for the lamp.

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 04-21-2015 08:01 AM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
Marcel: I know. I thought so as well. I can tell you that for 50 years the old 110 volt Simplex mono sound system ran very hot and had more troubles than any other 50 systems until I put the buck/boost transformer on it. Instant cure. Marquee bulbs failed at 125 per week. I moved to 140 volt bulbs.

 |  IP: Logged

Scott Norwood
Film God

Posts: 8146
From: Boston, MA. USA (1774.21 miles northeast of Dallas)
Registered: Jun 99


 - posted 04-21-2015 09:00 AM      Profile for Scott Norwood   Author's Homepage   Email Scott Norwood   Send New Private Message       Edit/Delete Post 
They make 140v bulbs?

Question on Steve's device: wouldn't this trip a GFCI outlet?

 |  IP: Logged

Steve Kraus
Film God

Posts: 4094
From: Chicago, IL, USA
Registered: May 2000


 - posted 04-21-2015 03:15 PM      Profile for Steve Kraus     Send New Private Message       Edit/Delete Post 
Yes, I suppose one could have relays on both inputs with 120V coils wired between the opposite side and neutral.

Yes, Scott. I never tried it but it certainly should trip because they compare current going out the hot to current coming back on the neutral. When they are not in balance it means current is leaving the hot somewhere and rejoining the system where neutral is grounded at the breaker panel or someplace like that and possibly doing so because someone's body is in contact with both the hot side and earth.

 |  IP: Logged

Dave Macaulay
Film God

Posts: 2321
From: Toronto, Canada
Registered: Apr 2001


 - posted 04-24-2015 09:06 PM      Profile for Dave Macaulay   Email Dave Macaulay   Send New Private Message       Edit/Delete Post 
Just use a "double: breaker made for 208/240 load circuits - if one leg overloads it also pulls the other one open. It used to be common to see two breakers tied together with a wire, they had holes in the handles for that. Now disallowed and new breakers do not have the holes. The panel mount breakers on Strong consoles are easy to mount in a box and do have the holes.
140V bulbs are often used in rural areas, sometimes even called "farm bulbs" - the long distribution runs have less stable voltage than dense urban grids.
If your voltage is unusually high or low all the time, contact the utility and have it changed. I think +/- 8% is usually the limit. It's a simple fix, the step-down transformers all have taps that can be changed in a few minutes.

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.