Marcel Birgelen
Film God
Posts: 3357
From: Maastricht, Limburg, Netherlands
Registered: Feb 2012
|
posted 07-07-2013 04:56 PM
quote: Scott Norwood Is it common to put the entire projector on a UPS? That seems like it could get very expensive very quickly just to prepare for what should be a rather rare event. Do these theatres have generators as well, with the UPS just being there to allow time for the generator to start up and stabilize? I would think that there would be other issues with running a theatre during a power outage (no HVAC, emergency lights on in auditoria, no ticket machine/cash register, etc.).
It surely isn't common to put the whole projector on UPS. If you do that you will indeed also need to put all the other power-hungry stuff like amps on UPS to keep the show running.
If you're living in an area with unstable power, you might consider to have those things on UPS too, but in those cases, a big central UPS will quickly become an interesting option, that will also make a generator setup much easier. Still, the costs involved are horrendous and I've never seen such a setup in a cinema yet (which obviously doesn't mean it isn't being done).
HVAC is something nobody will put on a UPS. Even big data centers run their HVAC systems solely on generators. The short interval between the blackout and the time the generator kicks in should not be a problem.
Emergency lightning is, at least around here, required to have its own backup batteries and in case of a blackout.
Lightning, Auditorium lights, cash registers, etc. can all be on generator only. If the power goes out, people have to wait a minute or 5 before everything is back up, but I don't suppose that's a big deal. Lights should be back up once the generator kicks in.
| IP: Logged
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
Fred Schoenfeld
Film Handler
Posts: 49
From: PORTSMOUTH, VA
Registered: Aug 2004
|
posted 05-11-2014 02:20 PM
WHEN WE DECIDED TO RESTORE AN OLD 1945 SINGLE SCREEN HOUSE BACK IN 1987, I DECIDED TO INSTALL A 40KW GENERATOR (208 VOLT, 3 PHASE) POWERED BY A 200 HORSE FORD ENGINE, RUNNING OFF OF NATURAL GAS. COST OF THE UNIT THEN WAS AROUND $15,000. I WIRED EVERYTHING IN THE THEATRE, EXCEPT FOR HVAC AND HEAVY KITCHEN EQUIPMENT (WE ALSO HAVE FULL FOOD SERVICE) WITHIN THE THEATRE THROUGH THE TRANSFER SWITCH. AT THAT TIME WE HAD TWO 35 MM SYSTEMS THAT WOULD SHUT DOWN WHEN WE HAD A VERY SHORT POWER INTERRUPTION; SINCE THE GENERATOR HAS A 10 SECOND START DELAY.
I ALSO DECIDED TO INVEST IN A EATON 12KW BATTERY BACKUP (TRUE ALWAYS ONLINE) UNIT THAT WOULD KEEP EVERYTHING IN THE BOOTH ONLINE, EXCEPT FOR THE LAMPS.
THIS HAS WORKED VERY WELL AND SINCE CONVERTING TO DIGITAL 2 YEARS AGO, IT HAS SAVED OUR SHOWS FROM EVER BEING OFF SCREEN. I DON'T RECOMMEND THIS FOR MOST HOUSES, BUT SINCE WE ARE A HISTORIC, SINGLE SCREEN THEATRE, IT HAS PAID FOR ITSELF MANY TIMES OVER!
WE EVEN HAD A PERFORMANCE WHEN A HURRICANE HAD KNOCKED OUT POWER TO THE ENTIRE REGION! WE ALWAYS GET COMMENTS WHEN THE ENTIRE DOWNTOWN IS BLACKED OUT, EXCEPT FOR OUR OLD MARQUEE!
| IP: Logged
|
|
|
|
|
|
|
|
|
|
|
|
All times are Central (GMT -6:00)
|
This topic comprises 2 pages: 1 2
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion