Topic: Where Are They Now (Drive-In Heater)
|
|
|
|
|
|
|
Phil Hill
I love my cootie bug

Posts: 7595
From: Hollywood, CA USA
Registered: Mar 2000
|
posted 10-11-2003 07:40 PM
Steve, I was actually more concerned about hardware and the installation costs.
Both a 120-volt or a 240 volt system would be inherently safe if installed correctly. But, since there is no way to be certain that the same number of heaters would be on at the same time on both sides of the line in the 120-volt configuration, the big technical advantage of course is the automatic balancing of the load distribution in the 240-volt configuration. This is very important not only from a technical standpoint, but from a power cost consideration. Most power-bill rates for “industrial” installations are based “leg demand” and balance. Power companies don’t want someone to make their life difficult by presenting highly unbalanced loads on their systems.
By way of an example, let me put this down so I can understand what I want to say...
Assumptions: 1) 120/240 volt single phase "split" system. 2) There are 200 heaters in this Drive-In. 3) Each heater takes 600 watts. 5A@120V. 2.5A@240V. 4) We want the heaters in only 5 rows. Each row has 2 sections that feed from the center at the projection booth. Each section has 10 heaters. 20 "sections" total. The last heater in each section is 100 ft from the booth and the branch-circuit breakers.
Total Power for the heater system would be 200htrs x 600watts = 120kW. 1000 amps @ 120V…500 amps @ 240V. While the main panel and feeders would be sized the same there would be one less conductor and bus bars and connections on the 240V system since a neutral is not required. Each hot leg, and neutral, would still have to sized for the 500 amp rating…700CM copper?
Each row "section" would have a heater load of 10htrs x 600watts = 6kW. 50A@120V. 25A@240V. (20 sections = 120kW). Again, each branch circuit would still have to have the same size wire for the hot legs but no neutral. Assume no more than a 2% voltage drop at the last heater, the wire size would have to be min #8, #6 AWG copper. Also, since the last heater/post must still be able to trip the branch breaker (40Amp?) in case of a fault, that size wire would have to be carried all the way thru all the branch circuits.
That "extra" neutral conductor alone results in a 33% increase in hard costs. Not even taking in consideration of conduit loading/sizing, extra labor costs to install, etc. (Note: there still would have to be a ground conductor in both cases…3 vs. 4 conductors.
I like the idea of a 480-volt system, but I think that would be "pushing the envelope" …beside the codes get really weird once you get past to 300 volt mark. Although 480/277 3-phase might be an option.
About the grounding of the isolation/distribution transformers. If there is no reference to ground on the secondary, there exists a potential shock/electrocution hazard by way of 2 or more equipment faults such as a conductor "touching" a heater case and other one touching the pole. Some poor patron could be fried if they were to get across that. By grounding a leg, the system has a "reference" with which to draw enough current thru to trip the safety devices including the GFIs. Also it is wise for lightning protection or for insulation leakage currents and pri-sec xmfr failure.
The studio example you site is very common for avoiding hum and noise. But note, the center-tap is the ground reference.
Now that I have totally confused myself, I hope you can make out the jest of what I'm trying to say!
>>> Phil [ 10-12-2003, 08:43 AM: Message edited by: Phil Hill ]
| IP: Logged
|
|
|
|
All times are Central (GMT -6:00)
|
This topic comprises 2 pages: 1 2
|
Powered by Infopop Corporation
UBB.classicTM
6.3.1.2
The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion