» Film-Tech Forum ARCHIVE   » Operations   » Ground Level   » Movie theatre fined for locked emergency doors (Page 3)

 
This topic comprises 4 pages: 1  2  3  4 
 
Author Topic: Movie theatre fined for locked emergency doors
Brad Miller
Administrator

Posts: 17775
From: Plano, TX (36.2 miles NW of Rockwall)
Registered: May 99


 - posted 08-25-2013 03:41 PM      Profile for Brad Miller   Author's Homepage   Email Brad Miller       Edit/Delete Post 
quote: Mark Hajducki
The staggered evacuation would prioritise the areas near the location of the (suspected) fire based on information from call points and sensors. There would not be a standard plan for this.
Yes each screen can be individually triggered for this.

 |  IP: Logged

Scott Norwood
Film God

Posts: 8146
From: Boston, MA. USA (1774.21 miles northeast of Dallas)
Registered: Jun 99


 - posted 08-25-2013 03:56 PM      Profile for Scott Norwood   Author's Homepage   Email Scott Norwood   Send New Private Message       Edit/Delete Post 
quote: Mark Hajducki
It is strange how much the codes vary between country. In another thread I was surprised to find that weekly fire alarm testing was not required in the USA, as was testing the safety curtain daily in live theatres.
In general, testing a fire alarm in the US requires the cooperation of the local fire department. I don't know how it works in the UK, but a US fire alarm system in a commercial building does more than just trigger bells or horns--it typically signals the fire department, either through an alarm company or by triggering a Gamewell master box that is connected to the city or town fire alarm telegraph system. Testing this sort of system typically requires that a fireman and/or alarm company service man be present.

There is no way that a local fire department could deal with a test alarm from every commercial building in the town once per day. It would completely overwhelm them and would increase the response time for real alarms.

Thus, fire alarms in commercial buildings are typically tested semi-annually. There are plenty of internal self-tests in a modern alarm system and a "trouble" indication will be given (typically on a lighted panel) if something goes wrong in the meantime.

Fire extinguishers are typically inspected and tagged every year.

The staggered evacuation thing is becoming popular in the US for some reason. At my last job, I worked in an office building that had this sort of system. The alarm would sound on all floors, and a barely-audible synthesized voice would call for an evacuation on the floor where the alarm was triggered and the floors immediately above and below that floor. On other floors, it would tell people to stay in place and await further instructions. I realize that the purpose of this was to avoid congestion in the stairways, but the whole thing always made me nervous, and I am not sure that I would want to stay put in a burning building even if the synthesized voice told me to do that.

 |  IP: Logged

Leo Enticknap
Film God

Posts: 7474
From: Loma Linda, CA
Registered: Jul 2000


 - posted 08-25-2013 09:06 PM      Profile for Leo Enticknap   Author's Homepage   Email Leo Enticknap   Send New Private Message       Edit/Delete Post 
quote: Farnk Cox
"Remove bolts, padlocks and security devices from fire exits"? Really? It's illegal to have a lock, bolt or padlock on a fire exit door here. Even if nobody is in the building.
As Mark points out, the norm in England and Wales (Scots law differs in many ways from that in England, Wales and NI) is that it's OK to have fire exits secured, as long as no customers are in the auditoria and staff have adequate emergency exit provision (and are trained in its use). In the theatres I worked, chaining up the emergency exits was pretty much the last thing that was done by the last person to leave the building at the end of the night, and the first thing that was done by the manager or projectionist who arrived to open up.

The English law with regard to cinema regulation is a bit weird, to put it mildly. It has its origins in the Cinematograph Act 1909, which was essentially a kneejerk response to some nitrate fires and other nasty accidents caused by the hasty (and often jerrybuilt) conversion of stores, shops and other buildings into movie theatres. It set out certain safety requirements in broad terms, but put the responsibility for enforcing them onto town and city councils. The basic system that act put in place is still the one that operates today: in order to have the legal right to charge members of the public money to watch movies on your business premises, you need a licence from your local authority. That is granted after they come and inspect you, and one of the things that happens as part of that inspection is that the fire officer (a professional firefighter but who is acting on behalf of the council) visits the place and satisfies him/herself that your fire prevention (and first-line firefighting) infrastructure is up to scratch, and that staff are properly trained. If (s)he isn't satisfied, the council won't give you a licence (or will pull an existing one).

But some fire officers are more punctilious than others. I've been present at inspections where the place has been gone over with a fine tooth comb, right down to demands to inspect maintenance records for the extinguishers and alarm system, to a ten-minute walkaround, one or two questions, yeah, you're OK and I'm outta here.

Scott - some alarm systems here do make an automated phone call to the fire brigade if they are not reset after a set time has elapsed (e.g. 90 seconds), but on the systems I've worked with this function can be disabled for testing purposes.

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 08-26-2013 02:27 AM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
At the college where I work the fire alarm system is tested at 7 a.m. every Thursday. The fire brigade do not come out, as they do when the alarm is normally activated, but whether that's because the system for calling them is de-activated, or because they're told that it's a test I don't know. The latter would be better since it tests the calling system.

I haven't noticed it recently, but it used to be the case in some types of buildings that all chains and padlocks had to be hung on a board in clear view when the building was open, so that it could be seen if any were missing, and therefore a door possibly still locked.

 |  IP: Logged

Louis Bornwasser
Film God

Posts: 4441
From: prospect ky usa
Registered: Mar 2005


 - posted 08-26-2013 07:47 AM      Profile for Louis Bornwasser   Author's Homepage   Email Louis Bornwasser   Send New Private Message       Edit/Delete Post 
Delayed system has a fault in that many people will NOT operate a fire pull until they think they are safe. That means the alarm point will be away from the fire. "Smart" systems have the possibility of sending some people toward harm.

 |  IP: Logged

Andrew Thomas
Master Film Handler

Posts: 273
From: Pearland, TX, USA
Registered: Jun 2012


 - posted 08-27-2013 07:00 PM      Profile for Andrew Thomas   Email Andrew Thomas   Send New Private Message       Edit/Delete Post 
quote: Brad Miller
Andrew, I think you may be missing my point above, so I'll twist it around to better make that point.

So a business with front doors that do NOT have crash bars, but instead have deadbolts on the doors doesn't warrant a $10,000 fine?

To quote Will Smith..."awwww hell no."

But that isn't what happened here and isn't what you were calling for a $10,000 fine for. The doors had magnetic locks on them that were triggered by a relay for the panic bar. Apparently there was some problem and the panic bar didn't cause the maglock to release.

Unless there is evidence of actual negligence (like a lack of testing( or willful intent to keep the door locked no matter what, to suggest a $10,000.00 fine is ridiculous. The article gives no indication of negligence or intent on the part of theater management and so the $250 fine and negative publicity is probably an appropriate motivator to have the system fixed. I wouldn't have any issue with requiring the system to be tested and any errors to be corrected before those auditoriums could be put back into use.

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 08-28-2013 02:24 AM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
A system such as this should fail safe. If it works as you describe then a single sticking relay could cause a wrong side failure. I'd suggest two relays, with both n/o and n/c contacts sensed on both. If any of the four contacts changes from its expected state then the doors should be released. I'd also want to see this tested frequently, several times each day.

"The maglock system failed" really is nothing like a good enough excuse for people being trapped in a theatre building.

 |  IP: Logged

Pete Naples
Phenomenal Film Handler

Posts: 1565
From: Dunfermline, Scotland
Registered: Feb 2001


 - posted 08-28-2013 07:11 AM      Profile for Pete Naples   Email Pete Naples   Send New Private Message       Edit/Delete Post 
You'd be amazed at the number of DLP installations that aren't even connected to fire alarm for automated shutdown here, because the people who 'installed' the equipment don't understand things like relays, or didn't have the necessary bits to interface the 24v fire alarm with GPI on the server, or simply didn't have time. Even better are the places where unless the system is running content from the server, nothing happens on fire alarm. This is why my automation interface has a dedicated fire alarm input which is totally independent of the server. So if alternative content is running, you still have some form of shutdown on fire alarm activation. [Roll Eyes]

Once upon a time, not so long ago, it was not uncommon in smaller cinemas, say 1-3 screens, to have a system of hooks to hang the fire door chains on. Either in a very prominent place, such as beside the projectors so the staff would see straight away they were still on the doors, or as I have installed at some places, on hooks with electrical interlock. Chains not on hooks = projectors will not run.

I've never actually seen any kind of electrical fire door locking system which unlocks the doors on fire, what we see here are magnetic devices which are holding doors open, that release on fire, thereby slowing the spread of fire through the building.

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 08-28-2013 07:37 AM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
Thanks Pete. Digital equipment is being re-commissioned as we speak, or at least it is due to be. I'll check that this has been done, and ask for it to be tested before re-opening. It wasn't connected when the system was originally installed, but this was done after a while.

Here at the college we have a number of doors leading to fire escape routes which are held closed by maglocks which are supposed to release when the fire alarm is activated. At least one didn't when the system was first used after the building works were completed. I don't like it, and I wouldn't install it if it was up to me.

We also have a few of the doors in long corridors which are held open but automatically closed for smoke control.

 |  IP: Logged

Leo Enticknap
Film God

Posts: 7474
From: Loma Linda, CA
Registered: Jul 2000


 - posted 08-28-2013 11:46 AM      Profile for Leo Enticknap   Author's Homepage   Email Leo Enticknap   Send New Private Message       Edit/Delete Post 
quote: Stephen Furley
Here at the college we have a number of doors leading to fire escape routes which are held closed by maglocks which are supposed to release when the fire alarm is activated. At least one didn't when the system was first used after the building works were completed. I don't like it, and I wouldn't install it if it was up to me.
That's because (I was told) if you leave a maglock energised without releasing it for too long, it retains its magnetic properties after the power is switched off. There are maglock fire doors in our building at the university which release and close if the alarm is activated, which we're under instructions from Estates Service to release and close manually over each weekend to prevent this from happening. If you just leave them on 24/7 for weeks and weeks, they will no longer lose their magnetic 'stickiness' when the power is cut.

 |  IP: Logged

Frank Cox
Film God

Posts: 2234
From: Melville Saskatchewan Canada
Registered: Apr 2011


 - posted 08-28-2013 11:57 AM      Profile for Frank Cox   Author's Homepage   Email Frank Cox   Send New Private Message       Edit/Delete Post 
I have seen a fire exit door in a large store with a sign stating that when you push the bar an alarm will sound and the door will open fifteen seconds later.

This seems unnecessarily complex and failure-prone to me, when you're dealing with a potentially life-threatening event. If there is a fire, explosion, release of poisonous gas or whatever, I want to get out now, not fifteen seconds from now.

Some years back a chap I knew at the time was running a fixed highway weigh scale (checking for overweight trucks) when the shelf in the bathroom fell off of the wall, a bunch of stuff got smashed on the floor. A container of bleach got mixed with a jug of toilet cleaner and the room filled up with poisonous gas. He had to crawl out of the building on his hands and knees and just barely made it out alive. Afterward, the badge on his cap was visibly corroded, and all of the electronics were eaten out of the scale; even the doorknobs were corroded.

There was no fancy fire exit system there and that's good. A fifteen second wait in those circumstances would have killed him.

 |  IP: Logged

Stephen Furley
Film God

Posts: 3059
From: Coulsdon, Croydon, England
Registered: May 2002


 - posted 08-28-2013 03:21 PM      Profile for Stephen Furley   Email Stephen Furley   Send New Private Message       Edit/Delete Post 
quote: Leo Enticknap
That's because (I was told) if you leave a maglock energised without releasing it for too long, it retains its magnetic properties after the power is switched off. There are maglock fire doors in our building at the university which release and close if the alarm is activated, which we're under instructions from Estates Service to release and close manually over each weekend to prevent this from happening. If you just leave them on 24/7 for weeks and weeks, they will no longer lose their magnetic 'stickiness' when the power is cut.


I'm somewhat skeptical that you'd ever get strong enough residual magnetism to prevent a door from being opened with a good shove, but I'm prepared to be convinced otherwise. However, that was not what happened in this case, the door released as soon as the maglock was turned off with a key. Of course, most people would not have had the switch key, it's a special one, not the standard 'fish' one; looks like a filing cabinet key. Also, even if you have the key you wouldn't want to grope around in a smoke-filled corridor lit only with emergency lighting to find the switch to put it in. There's another door next to the one in question which should not release on the fire alarm, it's not part of an escape route and leads into our server room where you wouldn't want people to go, and from which there's no other means of escape. I suspect that the lock had either been wired up wrongly in error, or more likely these days, mis-programmed. These things seem to be software controlled these days.

These locks don't even release if power is lost; there's a lead-acid battery in each controller box which keeps them energised for some time, I think it's at least an hour, without mains power.

These things are installed by security companies who seem to be more concerned with keeping people out of places than with letting them get out in an emergency. I have no objection to the small maglocks which hold a door open and release to allow it to close for smoke control, but I don't like the large ones which hold a door closed, and are supposed to release it to open in an emergency.

 |  IP: Logged

Mark Hajducki
Jedi Master Film Handler

Posts: 500
From: Edinburgh, UK
Registered: May 2003


 - posted 08-28-2013 04:24 PM      Profile for Mark Hajducki   Email Mark Hajducki   Send New Private Message       Edit/Delete Post 
Do the maglock doors have emergency release points (green coloured fire alarm call points) that open the door and alert security?

 |  IP: Logged

Leo Enticknap
Film God

Posts: 7474
From: Loma Linda, CA
Registered: Jul 2000


 - posted 08-28-2013 04:54 PM      Profile for Leo Enticknap   Author's Homepage   Email Leo Enticknap   Send New Private Message       Edit/Delete Post 
quote: Stephen Furley
I'm somewhat skeptical that you'd ever get strong enough residual magnetism to prevent a door from being opened with a good shove...
Sorry - probably didn't explain myself very well. The fire doors I was talking about (mainly ones in corridors) are held open on the maglock: if the fire alarm is activated, the power supply to the maglock is cut, and the door is then supposed to be released and swing shut. The thinking is (same principle as with vacuum brakes, I'm guessing) a power supply is needed to maintain the system in a potentially unsafe state. No power = the system reverts to a safe state. If the fire alarm goes off when no-one is around to give the doors a good shove should they stick (e.g. in the middle of the night), then residual magnetism in the door maglock could be a problem, I guess. Whenever I've pressed the trip buttons on the top of the maglocks (which momentarily cut the power supply), they've always released the doors instantly, and so I'm hoping that Estates Services are just being paranoid by telling us to release them over the weekends.

 |  IP: Logged

David Buckley
Jedi Master Film Handler

Posts: 525
From: Oxford, N. Canterbury, New Zealand
Registered: Aug 2004


 - posted 09-08-2013 06:25 AM      Profile for David Buckley   Author's Homepage   Email David Buckley   Send New Private Message       Edit/Delete Post 
quote: Stephen Furley
If it works as you describe then a single sticking relay could cause a wrong side failure. I'd suggest two relays, with both n/o and n/c contacts sensed on both. If any of the four contacts changes from its expected state then the doors should be released.
Using relays safely is a well understood artform, and is widely practiced around industrial machinery. One has to use the right components assembled in the corrct manner, and there are a fair number of standards and regulations in the field.

It is force guided relays that makes reliable (or at least failure detectable) relay systems possible.

Have a gander at Safety Related Control Systems

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 4 pages: 1  2  3  4 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.