Posted by Steffan Laugharne (Member # 800) on 05-09-2001, 01:57 PM:
 
I've been installing Strong CNA200 automation with Dolby CP650's. In a number of multiplexes, when the fire alarm goes off (contacts that are NO become closed)and the projector shuts down. This is fine when films are running, but if any theatres are between performances with Non-Sync playing, the CP650 does not switch to mute.

I have two questions;

a) has anybody else encountered this and
b) is there any way with inside front panel dip switches that the processor can be switched to a film sound format on fire alarm shut down(the idea being that if the projectors are stopped then no sound will be routed through the processor should one be in Non-sync mode).

All the best

Steff
 


Posted by Steve Guttag (Member # 268) on 05-10-2001, 12:34 PM:
 
Yes, the CNA automations can do a "Fire Stop"...this was not an original feature but has been added on the current units. If you read your manual, it should tell you which dip switch to set for "FIRE STOP"...one of the features of "Fire Stop" is that it will put out a "Mute" pulse to the cinema processor.

Steve

------------------
"Old projectionists never die, they just changeover!"
 


Posted by Steffan Laugharne (Member # 800) on 05-10-2001, 02:08 PM:
 
Hi Steve

We've activated this function and wired accordingly on all installs, but it seems the CP650 still will not come out of non-sync. Is there a function in the CNA200 which will allow selection of a film sound format on fire alarm stop? Since the projetor stops, this will mute the sound, and if a theatre is between performances on non-sync this will also mute the sound by switching to a film format. It seems there may be a glitch in the CNA software or automation interface? Has anyone else had this particular problem?

We've overcome this on screens with CP45's by linking the mute terminal on the break out board in the CNA to Mono (since the Mute fuction does not exist on this processor).

Steff


 


Posted by Pat Moore (Member # 380) on 05-10-2001, 04:13 PM:
 
Steffan;

I'm checking with our developers and will confirm, but I think what you say is correct.

What might be happening is that since these systems are already in an Intermission mode, there is no film presentation to stop.

I think the fire stop input is effective only if the automation is actually running a program. The normal intermission mode, such as you describe, is a state where the automation is NOT running any program, so there's literally nothing to stop.

I'll post back when I get some more information.

Pat
 


Posted by Pete Naples (Member # 761) on 05-10-2001, 04:53 PM:
 
Stefan,

I observed precisely this condition on a CNA200/CP650 install, the CNA does not mute the sound if it's in intermission. It really needs to as some fire officers are very unhappy about this.

At least the CP650 doesn't stay in mute at every other lens change like the CP500 is want to do....
 


Posted by Steve Guttag (Member # 268) on 05-11-2001, 08:25 AM:
 
Ah Stefan,

I didn't read your message properly, I apologize....I missed the part where the problem is when the fire alarm goes off while in Non-Sync.

If you have a master music system with distribuition amps...why not have a relay hooked to your alarm that interrupts the music feed to the DA system? This will kill it in the lobby and all theatres.

Steve

------------------
"Old projectionists never die, they just changeover!"
 


Posted by Steffan Laugharne (Member # 800) on 05-12-2001, 03:33 AM:
 
Hi Steve

Unfortunately or fortunately (depends on your POV), the chain that I install for follow the usual UK practice of having separate CD players for each screen (such that non-sync music may be tailored to the mood of the feature)so I'd have to inturrupt the non-sync in each sound rack which I don't really want to do.

It would be nice if there were a fix within the CNA200 involving dip switches/ software upgrade.
 


Posted by Steve Guttag (Member # 268) on 05-12-2001, 09:10 AM:
 
Nice comeback!

Steve

------------------
"Old projectionists never die, they just changeover!"
 


Posted by Gordon McLeod (Member # 33) on 05-12-2001, 09:40 AM:
 
I don't have my book with me but I believe you could use a blocking diode from the firealarm and a single relay to control the mute function directly
 
Posted by Rick Long (Member # 213) on 05-19-2001, 10:23 AM:
 
Might not a simple solution be to have the normally open contacts of the fire-alarm panel feed a relay that would interupt the a.c. feed to the non/sync source?
Simpler still, of course, would be to feed the ac for the non/sync source through the normally closed contacts of the alarm panel, provided that it is rated for the current and voltage required.


 


Posted by Steffan Laugharne (Member # 800) on 05-19-2001, 04:21 PM:
 
Rick,

This would be an option if we didn't have a CD player in each screen. This idea works well for the other chain I install and service since there is a distribution amp for non-sync. The other problem with your plan is that each CD player is fed from the same power strip as the processor and amplifiers. I wouldn't like the supply to the amps to be broken due to the fire alarm in case the supply was resumed. So I still need a solution to the shutdown problem!!!!!!!

All the best chaps


Steff
 