Posted by Paul G. Thompson (Member # 655) on 07-08-2002, 03:23 AM:
 
Here is someting I ran across I found kind of interesting. It goes back to 1991, and some articles were ammended in 1996.

Check out Article V which deals with Nitrate film. It looks like the City of Yonkers, New York really has some real clomps on this stuff.

Here is an excerpt:
.....................................................................
B. Nitrate film in any projection room or rewinding room shall be kept as follows:

(1) Up to forty (40) pounds of film [eight thousand (8,000) feet of 35-mm film] may be kept in I.C.C. shipping containers or an approved cabinet in each room.

(2) If the amount of film on hand exceeds forty (40) pounds, an approved cabinet shall be provided, in which the amount of film in excess of forty (40) pounds shall be kept.

~ 24-68. Special room required for examining, piecing and repairing film.

All examining, rewinding of reels, repairing or piecing together of flammable motion-picture films shall be done in a booth, room or compartment used for no other purpose and separated from the rest of the building by fireproof partitions and self-closing fire-resisting doors.


~ 24-69. Flammable cement or liquid storage restricted.

No celloidin, amylacetate or other similar flammable cement or liquid in quantities greater than one (1) quart shall be kept in a room where flammable motion-picture films are stored or repaired.

.....................................................................

Check out Article IV. Looks like a projectionist really has to jump through a million hoops to get a license to operate the booth in that area. Hmmmm.....maybe professionalism will finally make a come back.

http://www.cityofyonkers.com/code/ycc024.html

OK, I am convinced Nitrate film is some nasty stuff. But the question I have is: Just really how nasty is it? Personally, I wouldn't touch that stuff with a 100 meter pole.

Joe, I watched your training videos on it, and that also adds to the idea that I don't want anything to do with Nitrate film. Am I just being paranoid, or what?

Sorry, Brad. When I try that "click here" thing, it turns to worms.


 


Posted by Leo Enticknap (Member # 534) on 07-08-2002, 04:46 AM:
 
Nitrate film is potentially very nasty, but if you understand what it does and take common sense precautions it won't hurt you.

We deal with substances which if misued can kill us all the time. The electricity wired all over our homes and workplaces, for example. In our cars we spend hours sitting 3-4 feet away from several gallons of petrol which, if it is ignited anywhere other than inside the cylinders of the engine, will produce a Kentucky fried driver. Yet very few people get burnt alive in their cars or electrocuted in their homes. When nitrate was in regular use in cinemas all over the world there were very few accidents relative to the number of workplaces involved, and the accidents which did happen were usually caused (either directly or indirectly) by human error.

Cellulose nitrate film has the following properties which make it distinct from most other combustible substances:

From this it will be clear that cure is to all intents and purposes impossible, so safety precautions are designed to prevent the stuff igniting in the first place, and if it does ignite to manage the burning process so that it doesn't endanger anyone.

An archive has a much easier job than a rep cinema which still shows nitrate, because the former does not need to expose the film to any significant heat source. The basic rules of thumb are as follows:

In some ways cinemas need to be even more anal. I know of only one cinema in the UK which is licensed to show nitrate and still does so 2-3 times per year - it's really not common. The problem is, of course, that in projecting it you have to expose the film to serious heat, i.e. from the projector's xenon lamp. But the same principles apply - store safely, prevent ignition, prevent risk to life from burning film. In projectors, preventing ignition includes things such as liquid-cooled gates, heat filter glass and fire cutters on magazine manifolds, whilst preventing risk from burning film includes fire shutters on portholes, enclosed spool magazines on projectors and providing two fire exits from the booth (again, one of them directly to the exterior of the building).

These precautions also apply to transporting nitrate as well. Use a refrigerated and armoured truck, do not carry too much nitrate in one trip and move it in fire-retardant boxes. Should a fire break out, the truck needs to be strong enough for the driver to have time to stop and get out.

Frankly, private collectors hold the stuff at their own (considerable) risk. Were there to be a fire involving nitrate in your house, then no way would your insurance company pay up if they found out it was there... that is, if you were still alive to make a claim.


 


Posted by Peter Kerchinsky (Member # 1098) on 07-08-2002, 05:36 AM:
 
Hey Paul
If I hear a loud boom coming from up Mt. Vernon way I'll know you been messing with that stuff. (just kidding).
I worked a couple of booths in MA. and both had very bad burn marks on their ceilings. When I inquired about this I was told by the working projectionists the burn marks were from nitrate fires back when. I was told by them when the film burned they immediately scramed out of the booth, the ports were sealed off and they just let it burn itself out.
We did set some nitrate off on a roof once to dispose of it and believe me it goes up fast.
Someone told me once that when nitrate goes bad, reddish in color, it acts like dynamite.
 
Posted by Leo Enticknap (Member # 534) on 07-08-2002, 06:51 AM:
 
quote:
Someone told me once that when nitrate goes bad, reddish in color, it acts like dynamite.

When nitrate is first manufactured, it is prone to rapid combustion (burning). My chemistry is a bit hazy on the details of the decomposition process, but suffice as to say it starts out as nitrocellulose and gradually turns into a substance similar to nitroglycerine - an explosive. According to Chambers' Dictionary...


In other words, 'fresh' nitrate will produce flames and fumes if ignited, whilst decomposing nitrate will also produce mechanical force.

'Powdery' nitrate (second stage decomposition) isn't significantly more volatile than nitrate which is still serviceable, but once it starts going sticky and sludgy (third stage) then you really need to watch out. In particular, do not attempt to dispose of it by burning - it could be the last match you strike...


 


Posted by John Pytlak (Member # 331) on 07-08-2002, 07:56 AM:
 
Here's the Kodak publication about cellulose nitrate film:
http://www.kodak.com/US/en/motion/hse/safeHandle.jhtml

Look at the three nitrate fire videos in the "Video" section of Film-Tech to get an appreciation of how fast and furious nitrate burns. The toxic gasses have been the usual killer.
http://www.geocities.com/soho/square/5632/nitratefires.html
http://www.clevelandclinic.org/act/frames/chp3/chp3_1.htm
http://www.clevelandclinic.org/act/frames/chp3/chp3_2.htm

------------------
John P. Pytlak, Senior Technical Specialist
Worldwide Technical Services, Entertainment Imaging
Research Labs, Building 69, Room 7525A
Rochester, New York, 14650-1922 USA
Tel: +1 585 477 5325 Cell: +1 585 781 4036 Fax: +1 585 722 7243
e-mail: john.pytlak@kodak.com
Web site: http://www.kodak.com/go/motion
 


Posted by Leo Enticknap (Member # 534) on 07-08-2002, 08:32 AM:
 
In addition to the archive fires cited on David Lemieux's website there was a big one at a cinema in Dallas in 1950 or 51 in which one fireman was killed and several others were badly hurt by fume inhalation. Apparently the local Fire Department believed that the conversion to safety film was complete and so did not use breathing apparatus. I came across an article describing it in the British Film Institute library a few months ago - will have a look through papers in the next few days to see if I can find it.

There was also a serious fire at Hendersons in South London, a lab specialising in archival duplication work, in the early '90s. In this case the fire retardant vaults did their job and no-one was hurt. But a lot of valuable film was lost, though, including the camera negatives of Kind Hearts and Coronets and Whisky Galore, which were being reprinted for an Ealing retrospective at the Barbican Cinema...
 


Posted by Paul G. Thompson (Member # 655) on 07-08-2002, 12:42 PM:
 
Thank you, gentlemen.

I'll just leave the Nitrate film in the hands of the professionals who have the proper facilities and equipment in place and know what the hell they are doing.

Although there may still be some booths in the world that can safely handle the projection of Nitrate film, there are probably hundreds of booths that cannot even though they were designed for it. However, due to building and equipment deterioration, they may not be able to safely handle it today without going through the expense of getting the booths and the equipment up to specifications.

Most fire shutters have been removed from the projectors. Those shutters would drop if the projector would fall to half-speed. The old Simplexes and even the older XL's had a loop trip mechanism that would immediately close the fire shutter, along with other machines as well.

All that equipment has been removed from most of the projectors because they were troublesome. The magazine fire trap rollers are more than likely worn out if they are still in use, or they might have been replaced with plastic rollers. I doubt if the extremely worn steel rollers or the plastic rollers would keep the fire from entering the magazines. That's where the real problems could start.



 


Posted by John Hawkinson (Member # 1135) on 07-08-2002, 11:05 PM:
 
Funny you should mention Yonkers, Paul.
Are you aware that it's adjacent to the city of Mount Vernon, NY? What a coincidence.

--jhawk
 


Posted by Paul G. Thompson (Member # 655) on 07-08-2002, 11:15 PM:
 
John, I have had some weird things like that happen now and then.

And yet, I can relate some extremely weird stories that have happened (which most would consider coincidence) to me with people, places, and things, some of which to this day make my hair stand on end. The latest one happened yesterday, but I won't go into it. It's personal.


 


Posted by Josh Jones (Member # 447) on 07-09-2002, 03:38 AM:
 
Paul, dont you mean E-7's, not XL's. The xl's did indeed have fire shutters, but I dont remember them ever having a lost loop device.

Josh
 


Posted by Paul G. Thompson (Member # 655) on 07-09-2002, 04:15 AM:
 
Josh, the old XL's I got from Dolby Labs (very very low serial numbers, with a nut on the end of the shutter shaft) were equipped with loop trippers. When I rebuilt them, I took them off and tossed them in my Simplex Bone Box.

Quite honestly, they were the only XL's I have seen that were equipped with them. I am not sure when the first XL was built, but I know they were in the 3 digit serial numbers. 2** comes to mind..., so that had to have been around 1952, about 1 year or less after the Nitrate film was discontinued by Kodak. In the old Capitol Theatre in Manitowoc, Wisconsin (my home town) is where (in early 1952) I saw my first 35mm projection booth, and it had new projectors. Simplex XL's....with Brenkert Enarcs behind them. The XL's were sitting on top of the RCA-9030 sound heads, and had a WHOPPING 25-watt vacuum tube sound system, complete with the very pretty blue bulbs in a cage. I just turned 12 years old then. Of course, at the time I did not know what a loop tripper was even if it bit me in the ass.

Damn....I am getting old. Seems like 1952 was yesterday.


 


Posted by Howard Johnson (Member # 62) on 07-09-2002, 05:40 AM:
 
Another thing Paul, if you breath in the fumes from a nitrate fire they combine with the moisture in your lungs to form nitric acid! I last showed nitrate when we had "Dark Eyes Of London" starring Bela Lugosi ! It arrived for a sunday one day show in 1963. I noticed it had a distinct smell and was in 1000 foot cans I think we ran it in the short reels and did not bother to join them as it was only one day. The chief projectionist had to give up smoking in the box for the day. Although the box had fire shutters and firetraps on the projectors I think that it was illegal to show it even then. That film had our utmost attention for the day!!
 
Posted by Paul G. Thompson (Member # 655) on 07-09-2002, 02:12 PM:
 
Howard, I'll bet the chief projectionist didn't have too much of a problem laying off the smokes. He was probably so nervous running the Nitrate print that the slightest abnormal sudden noise would have caused him to jump out of his skin. Undoubtedly, he would have filled his shorts at the same time.

The lungs being consumed by Nitric Acid? That has to be a very painful and horrible death. No Thanks, not today.

Josh, the Simplex XL made its debut in 1949. Maybe the ones I got from Dolby Labs could have been 1950/1951 vintage. They sure were nice machines...


 


Posted by Stefan Scholz (Member # 147) on 07-09-2002, 04:43 PM:
 
It's no fun to burn nitrate. I carelessly projected my beloved 1942 swing music film from Germany, showing the large Ufa film orchestra with 40+ violins, 6 grands etc. Gorgeous piece of music. Ran nicely on approved projectors for some time. Those were converted to 70 mm, and when a friend asked to watch it, I used the projector used for "commercial film runs" - modern piece of electronic. Off course cold light mirror and heat filter, but no forced air gate cooling, and no spool boxes. It happened as it must happen, film broke, 4 turns of the shutter before the safety switch operated, film caught fire, just by the absorbed visible light of the 2.5 k lamp. The resst ist imaginable.
Luckily 20" concrete ceiling and large air volume with open doors and windows. So the stuff burnt nicely with a hot flame.
3 hours of cleaning from ashes, and a brown ceiling were the results. The split spool (another faux-pas) was thoroughly glowed.
Demages, a melted cover on the SDDS reader's cameras.
This was great luck I had.
After 30 second the 1900 ft were history...just the polystyrole core burning with black fumes.
Sorry, but it had to happen this way! Extremely careless, and dangerous, what I was doing to save some 2 minutes of conversion time back to 35 mm on the large machines.
Nitrate correctly handeled, meaning forced air cooling of the film in the gate is a very nice thing. With forced air cooling the film could stay over an hour in the gate with shutter open at 60 Amps without going out of focus. Tests at Bauer factory indicated, that with higher currents the film just decompensates in the gate, but the temperature never reached igniting level.
Taking care helps to prevent fire. The most careless hanling I have seen was an old private collector. His beloved nitrates were spliced on 6000 ft reels, and sitting on the floor in his basement booth. He was running a standard Victoria 5 without any safety measure, not even cold light mirrors. What would happen, if the reel caught fire, and some 100 lbs of nitrate behind that in a basement, with probably 20 guests. ... Better not to think of.
He told us, he encountered just 2 fires, which were cut off with a pair of scissors. So in two prints, about 6 ft were missing.


 


Posted by Paul G. Thompson (Member # 655) on 07-10-2002, 02:22 PM:
 
Check out the link below....and select the last two pictures of the vault exploding and burning.

I think I still will leave Nitrate film in the hands of the professionals....
http://www.geocities.com/soho/square/5632/nitratephotos.html
 