) and future needs.
quote:You still whining about that relay, Paul?
from Paul T:
And be advised....if any of this equipment does not have a UL certification... be prepared to spend alot of time finding out the UL info the contractor/inspector wants.
code:(*) For what it's worth, the only way I see to get to Article 647 from Article 530 is a reference in 530.11 "Permanent Wiring" permitting "communication circuits; audio signal processing, amplicfications, and reproduction circuits; Class 1, Class 2, and Class 3 remote-control or signaling circuits and power-limited fire alarm circuits shall be premitted to be wired in accordance with Articles 640, 725, 760, 800." Why is this relevent/interesting? Well, mostly it's not, but Article 640 ("Audio Signal Processing, Amlification, and Reproduction Equipment" defines "Technical Power System" as "An electrical distribution system with grounding in accordance with 250.146(D), where the equipment grounding conductor is isolated from the premises grounded conductor except at a single grounded termination point within a branch-circuit panelboard, at the originaging (main breaker) branch-circuit panelboard, or at the premises grounding electrode." Maybe I'm reading that wrong, but that seems to imply to be incompatible with the idea of "technical power" meaning 60V/120V balanced power. (250.146(D) permits isolated receptacle grounds not tied to the closest panelboard but instead terminating at some central grounding location)(1) All 15- and 20-ampere receptacles shall be GFCI pro-
tected.
(2) All outlet strips, adapters, receptacle covers, and face-
plates shall be marked with the following words or
equivalent:
WARNING--TECNICAL POWER
Do not connect to lighting equipment.
For electronic equipment use only.
60/120 V. 1{phi}ac
GFCI protected
(3) A 125-volt, single-phase, 15- or 20-ampere-reated recep-
tacle outlet having one of its current-carrying poles
connected to a grounded circuit conductor shall be lo-
cated within 1.8m (6 ft) of all permanently installed
15- or 20-ampere-rated 60/120-volt technical power-
system receptacles.
(4) All 125-volt receptacles used for 60/120-volt technical
power shall have a unique configuration and be identi-
fied for use with this class of system. All 125-volt,
single-phase, 15- aor 20-ampere-rated receptacle outlets
and attachment plugs that are identified for use with
grounded circuit conductors shall be permitted in ma-
chine rooms, control rooms, equipment rooms, equip-
ment racks, and other similar locations that are re-
stricted to use by qualified personnel
I have been shocked by 70 V lines....