Posted by Antony Barlow (Member # 9774) on 07-18-2017, 01:57 AM:
 
Hi,

I want to connect the 12v fire alarm to the fp25. Am I correct in assuming I need the alarm to go into a 24v relay then out to the motor stop and douser on in the terminal strip. The lamp is a manual switch

Thanks
 
Posted by Steve Guttag (Member # 268) on 07-18-2017, 07:18 AM:
 
Depending on if you have an FP25D (mechanical) or FP25E (electronic intermittent), your connection options vary. But essentially, yes, you would need a set of "dry contacts" to provide a "stop" command to the projector.
 