Posted by Taylor Goins (Member # 9458) on 09-08-2016, 09:59 PM:
 
Hey! Hope this is appropriate for this section.

I've learned how to set cues for the projector and lamp to automatically turn off when the movie is over. But is there a way to set cues to make the projector and lamp turn ON automatically? There are "Lamp On" and "Projector On" cues... I've tried them, but they just don't work. "Lamp On" does if the projector is already on. But "Projector On" never works. Any tips or advice would be great. Thanks!
 
Posted by Carsten Kurz (Member # 5396) on 09-09-2016, 10:27 AM:
 
I have seen this on a new NC900C installation as well. A Projector-On was configured, but did not work. Obviously, as the series-2 library does not support this as a generic function.

Here is how I solved it:

http://www.film-tech.com/cgi-bin/ubb/ultimatebb.cgi?ubb=get_topic;f=16;t=002010#000000

- Carsten
 
Posted by Mark Gulbrandsen (Member # 72) on 09-11-2016, 06:42 PM:
 
The projector on function on the NC-900 may have been disabled because of the mercury type lamps it uses. Everything else works. Next time I'm at a site with one I will will try that cue...

Mark
 
Posted by Steve Guttag (Member # 268) on 09-11-2016, 07:48 PM:
 
The projector ON function remains working for me on my NC900s with current software/firmware. Including on a projector installed 7/16. Again, I often have to double-send NEC cues for reliability.
 
Posted by Mark Gulbrandsen (Member # 72) on 09-13-2016, 01:51 PM:
 
I think most of the issue that people have sending cues to NEC is that they do not wait until after the lamp is done lighting. During the "Lamp Lighting" sequence on NC-900, NC-1200 and NC-2000 you can not communicate at all with the projector and ask it to process any other commands, if you send then they will be ignored. The NC-900 takes even longer although I have never actually timed it out. I want to say about 50 seconds though. I always tell customers to let the lamp warm up for at least 90 seconds before any image hits the screen anyway just because of the mercury lamps. How they choose to automate that in is their choice.

Mark
 
Posted by Steve Guttag (Member # 268) on 09-13-2016, 02:56 PM:
 
It isn't just the lamp-on cue Mark...ANY cue will get the NEC a thinkin' And while it is pondering its current task, it will not buffer in another one. But I've also found that without a double cue to NECs, they are just plain unreliable on their cues. It doesn't cost anything to double-cue (from an automation). It wouldn't surprise me if part of the problem with Ethernet commands is the port opening/closing consuming some cues. I know that the JSD100 had problems with that too. A server driven cue isn't as likely to be a problem since the server and projector are having a continual chit-chat.
 
Posted by Mark Gulbrandsen (Member # 72) on 09-13-2016, 07:04 PM:
 
I never have had any issues cueing once the lamp is lit. I'd hear about that right away if it happened very often...
 
Posted by Carsten Kurz (Member # 5396) on 09-27-2016, 05:28 PM:
 
I never had that cue issue between a Doremi and NC900. I usually place my cues very dense.

- Carsten
 