Posted by John T. Hendrickson, Jr (Member # 849) on 07-02-2001, 10:45 AM:
 
It's that time of year in our neck of the woods- hot and humid days with the ever present chance that our power will go out due to strong storms or power interruptions due to heavy demand.

We experienced two interruptions over the weekend. Fortunately, and as luck would have it, I reveiwed our booth procedures with the operators at a Saturday morning meeting, so everything went smoothly.

I'm curious to know what your procedures are, not only from the standpoint of the booth, but down on the floor as well.

Also, our Director of Operations was present Saturday night and got some interesting comments from patrons (Are we going to see the show? Are you going to start the movie over? Where shall we go?).
Any anecdotes on your experiences?

If this topic was covered on a previous thread, my apologies.

 


Posted by John Pytlak (Member # 331) on 07-02-2001, 10:58 AM:
 
Safety of the audience is the first priority. So proper operation of emergency lighting systems and emergency public address notification should be checked on a regular basis. As far as the film and equipment, procedures for startup after a power outage vary with the type of equipment, but need to be followed to avoid film or equipment damage. I assume for platter installations, the audience is urged to wait out the outage if it is short, since the film needs to be run through anyway when the power is restored.

Do most theatres have surge suppressors or other protection against nearby lightning strikes? How many have backup generators or UPS units for critical electrical and computer systems?

------------------
John P. Pytlak, Senior Technical Specialist
Worldwide Technical Services, Entertainment Imaging
Eastman Kodak Company
Research Labs, Building 69, Room 7419
Rochester, New York, 14650-1922 USA
Tel: 716-477-5325 Cell: 716-781-4036 Fax: 716-722-7243
E-Mail: john.pytlak@kodak.com
Web site: http://www.kodak.com/go/motion
 


Posted by Jim Ziegler (Member # 86) on 07-02-2001, 12:32 PM:
 
When we loose power, our booth staff is instructed to get as many breakers off as possible before it comes back on, to minimize the damage a potential surge would do.
 
Posted by Jerry Chase (Member # 660) on 07-02-2001, 02:36 PM:
 
Jim has the right idea. The worst situation is where one leg of the power goes out. There is a great temptation to keep going, but 3 phase items can be seriously damaged. Air conditioning compressors are most at risk.

If there is a partial outage (some lights work, others don't, etc.) someone should race to the AC breakers and turn them off.

Surge supression at the main entrance makes good economic sense.

Audiences will usually sit for five minutes before coming out of a theatre, so informing them of the problem is usually simple. Anyone want to post their boilerplate speech for power outages?

 


Posted by Adam Martin (Member # 641) on 07-02-2001, 03:03 PM:
 
Previously posted somewhere else, here is a link for this thread ...
Emergency Procedures (pdf file)

And don't forget to turn off the popper ... hey, is something burning?

[I disclaim all liability resulting from the use of these procedures]


 


Posted by George Roher (Member # 91) on 07-02-2001, 06:05 PM:
 
The theatre I am currently working in always has problems with thunder storms and power surges. What usually happens is some of the movies will shut down, and others will switch to non-sync but keep running. With the insane layout of this complex it's a real chore to run around and get everything running properly again.

Yesterday there were thunderstorms and we had 4 power surges. In one instance Shrek switched to non-sync and it was a few minutes before sound was restored. The customers wanted the film "rewound", as they always do. A manager asked me to cut the film (already 10+ minutes into the feature) and restart it from the beginning but I had to say no. We were likely to have more power surges (which we did), and I was getting behind schedule as it was.


 


Posted by Jerry Chase (Member # 660) on 07-02-2001, 06:13 PM:
 
quote:
What usually happens is some of the movies will shut down, and others will switch to non-sync but keep running.

This is simply unacceptable equipment and automation design. I know it is a fairly common problem, but I can't think of a single good reason for it to happen. I fault the manufacturers on this one. A drop-out power pulse should be registered as that, and not as a change to non-synch cue.

 


Posted by Andy Muirhead (Member # 712) on 07-02-2001, 06:26 PM:
 
Here in Scotland this doesn't happen to much, but if there is an electrical storm nearby, it has us all running about everytime there is a dip in power. Normally power dips for a fraction of a second, which in some cases is enough for the xenons to go out.

As soon as the lights flicker, all staff run and check all screens. If we do find a xenon that needs restruck we have to wait for the bulb to cool sufficiently to restrike. we could change the tappings on the rectifier to give us a higher strike voltage, but we'd have to wait then for the rectifier to lose charge enough to work on it safely, so it's 6 and half a dozen! Never had any other probs, though, with automation changing to nonsync or anything else.

It's a bit mad though as we have four screens, with four independent projection rooms, so we do look a bit stupid wildly running about everytime the lights flicker!
 


Posted by Scott Norwood (Member # 30) on 07-02-2001, 06:55 PM:
 
We had some nasty thunderstorms in the Boston area this weekend. The lights in the theatre flickered occasionally on Saturday, but the only major problem was that one show of Pearl Harbor lost sound for a minute or so while the DTS unit rebooted and switched the processor (CP55) back into "aux" from non-sync. This got me to thinking: does anyone plug sound equipment into a UPS? I would have switched it into 04 manually, but this theatre has two booths and moving between them requires passing through an auditorium. By the time I heard about the problem with the sound, the DTS unit had finished rebooting and all was well.

If we had lost power, I would have just killed power to everything at the breaker panels until everything was back to normal; I assume that the audience would have been given apologies and passes.
 
Posted by Rick McCluney (Member # 642) on 07-02-2001, 11:02 PM:
 
I once had a manager, who will remain nameless, who experienced a brown out in mid show. He wanted to make sure that the film would be ready for the next show since he lost the show that he was running so he continued to run the projector at the reduced voltage. Needless to say that motor was dead within a couple of days.

Rick
 


Posted by Paul G. Thompson (Member # 655) on 07-03-2001, 12:47 AM:
 
I just make sure the projection equipment and computers are shut down. I never worried too much about the HVAC's. Being an old refrigeration man, I found most compressors can usually handle it, unless they were ready to go on the fritz. Compressors have high current cut-outs that sense rotor lock current in event the head pressure is too high for the compressor to restart. They will usually restart themselves just fine after the discharge line (high side) pressure drops when it bleeds off through the expansion valve or cap tubes.

However, if you can, shut them down anyway, before the power comes back on just to be safe side. One thing you don't want to happen - that is, in 3 phase applications, the return of only two of the three phases of electrical power.

Make sure you have all three phases before you attempt to restart them. This is easy to determine. Does everything come on? If it does, chances are you will be OK. If roughly about 2/3d's of everything comes on, you can safely say, "Houston, We Have A Problem", and you better scramble to shut down all your three phase units if you have not previously done so. Otherwise, you more than likely wind up toasting your HVAC compressors or any three-phase motor you have in the building.

Usually, if you just drop one phase, the motors will continue to run under these circumstances, but will shortly self-distruct due to overloading. Most 3 phase motors are very unforgiving about operating with one phase missing, unless they are impedance protected.

Although "phase rotation" is usually not that important for HVAC compressors, it is important for blower motors and three phase motor-generator sets.

We have had the power company apply power with phase rotation accidently reversed. Our MG set for the black stick carbon arc lamphouses ran backwards, and did not produce enough current to light a firefly. So happens the lamp vent was also a 3 phase motor. It ran backwards, too.

HVAC units don't really care if their compressors run backwards or not.

So, make sure all your motors are running in the correct direction. A squirrel cage tumbler will blow air no matter which direction it is running. But, if it is running backwards, the amount of air it will move is almost ziltch!

OK - wrong thread for this, but it still fits power bumps.


 


Posted by Sean McKinnon (Member # 612) on 07-03-2001, 01:04 AM:
 
If you are using a dolby cp-500 then you can set the default power-up preset to Sr-d or whatever that way if the power goes out for a second and the unit restarts it will not start in non-sync. This also means that at the beginning of the day you have to manually switch all the processors to non-sync.
 
Posted by Paul G. Thompson (Member # 655) on 07-03-2001, 01:28 AM:
 
Those "bumpity bump" power failures will ruin lots of things....
 
Posted by Steven Gorsky (Member # 603) on 07-03-2001, 01:58 AM:
 
On the CP500, instead of setting it to wake-up in SRD, set it to wake-up to the last format. This way it will come back to what ever was used last, and you won't have to change it to non-sync when opening.

Steven Gorsky
 


Posted by Sean McKinnon (Member # 612) on 07-03-2001, 02:29 AM:
 
You know youre right. Thats what I meant to say but its been a while since I set-up one so i forgot.
 
Posted by Mike Blakesley (Member # 26) on 07-03-2001, 02:44 AM:
 
Most of the power outages here are about 5 seconds long, during thunderstorms....just long enough to screw everything up.

Is there a UPS that would handle a platter system for such a short outage? Everytime we get one of these outages, the platter of course stops immediately but the projector continues to "coast" film onto the floor for a few seconds.
 


Posted by Paul G. Thompson (Member # 655) on 07-03-2001, 04:20 AM:
 
Mike, you got that right!
 
Posted by Jason Burroughs (Member # 68) on 07-03-2001, 09:06 AM:
 
I would think that any small office UPS would be sufficient for a platter system, and could very easily save some film during a power outage, triped over the power cord etc. The current draw on platters is not very much, and the UPS's are designed to handle suprisingly big loads, just a matter of the time limit. Even with an itty bitty one you should be ok.

Its VERY intrresting when the Power Co. loses a Leg, its happened to me twice. Fortunatly at the building I was at, the A/C compressors had protection circuitry to protect them from such a thing. However the elevator electronics did not fare so well, trapping of all people, the electrician, as we desperately searched for the main switch to the building. (this was in a new theatre before the grand opening)


 


Posted by John Pytlak (Member # 331) on 07-03-2001, 09:37 AM:
 
Paul Thompson said: "Make sure you have all three phases before you attempt to restart them. This is easy to determine. Does everything come on? If it does, chances are you will be OK. If roughly about 2/3d's of everything comes on, you can safely say, "Houston, We Have A Problem", and you better scramble to shut down all your three phase units if you have not previously done so. Otherwise, you more than likely wind up toasting your HVAC compressors or any three-phase motor you have in the building."

Do any theatres have permanently installed voltmeters (or at least indicator lights) at the main panel to indicate that all legs of the 3-phase power are present, and whether they are balanced?

My home is on a hill in a lightning-prone area (in 15 years, about 10% of the homes have had direct hits). When we had lightning rods installed on our roof, we also installed surge protectors in the main 200A electrical panel. Much of the lightning damage in our neighborhood came in through the power lines -- one neighbor had every electronic appliance in his house damaged when lightning hit an outdoor light.

IMHO, operating sensitive digital electronics without proper surge protection and UPS units is asking for trouble.

------------------
John P. Pytlak, Senior Technical Specialist
Worldwide Technical Services, Entertainment Imaging
Eastman Kodak Company
Research Labs, Building 69, Room 7419
Rochester, New York, 14650-1922 USA
Tel: 716-477-5325 Cell: 716-781-4036 Fax: 716-722-7243
E-Mail: john.pytlak@kodak.com
Web site: http://www.kodak.com/go/motion
 


Posted by Paul G. Thompson (Member # 655) on 07-04-2001, 12:55 AM:
 
What John was talking about makes good sense. Have lamps installed on the main power panel which indicates phase presence and phase balance. That is cheap insurance as compared to the amount of damage that will be done if three-phase motors start to "single phase" and burn up.

But beware (not of the above comment) some of the older buildings may have 3 phase closed delta. That type of power has a "wild leg" which is worthless to 115vac applications. If I recall correctly, that leg is about 177vac, referenced to ground. It is not normally used with anything except 3 phase motors. If you lost it, you would never know until it is too late.

It is best you do some research on what type of power you have, so you can act accordingly when an outage hits. If you have a power poll feeding your building, look at the transformer configuration.

If there are two small "pots" and one big "pot", (as the power company calls them) you probably have 3 phase closed delta. This type of configuration is obsolete. However, it is still around and you will find it in old buildings.

If you have 3 "Pots" all of the same size, more than likely have 3 phase open delta. This configuration is used in all new commercial construction these days, unless your area is still living back in the stone age.

Residential power is usually single phase. I have never seen or heard of three phase power being used in the average modest home.


 


Posted by William Hooper (Member # 71) on 07-04-2001, 11:38 PM:
 
The best reason to put a cheapo $20 home computer UPS on all electronics that you don't want to replace is: when there's a lightning strike, the UPS always buys the farm but the zap goes no further.

There have probably been exceptions, but we're also in a very lightning-prone area, & after making that discovery, the little cheapo UPS's are everywhere. Stick them upstream of the stuff in the soundrack & the platters. Lightning strike, splat goes the UPS, go get another one, OR: spend way too much time trying to figure out what's now acting flakey & intermittent after the strike.


 


Posted by Leo Enticknap (Member # 534) on 07-11-2001, 02:21 AM:
 
As well as UPS on the power supplies I'd also disconnect 'phone lines and antennas if there's a risk of lightning. The modem in my computer got zapped last autumn in a lightning storm - the PC was switched off and the power unplugged, but the modem was still connected to the 'phone socket. When I next came to use it I got a 'no dialling tone' error and there were signs of blackening around the jack. Even after replacing it I'd occasionally get the 'blue screen of death' in the middle of doing something until I upgraded the motherboard a few months later, so I guess that must have been affected, too.

The funny thing is, none of the 'phone lines are carried on overhead pilons in my neighbourhood - they're all underground. So I've no idea how the lightning got into the system.


 


Posted by Joe Redifer (Member # 3) on 07-11-2001, 02:52 AM:
 
I'll back up what Leo said. Just last summer a bolt of lightning decided to strike in my backyard and split a tree in half, just for fun. It damaged many, many things in the house. Every phone (and modem) was destroyed. I had to get a new motherboard for my computer. One VCR was rendered useless, as was one TV. My Dolby Digital/DTS receiver still works, but if the subwoofer is powered on it emits a HUGE thump whenever I press the MUTE button, or whenever Dolby Digital or DTS drops back to analog (such as when switching sides on a LoserDisc). Homeowners insurance paid for most of it, but not everyone can be that lucky.


 


Posted by Jerry Chase (Member # 660) on 07-11-2001, 09:18 AM:
 
Someday I'll get around to making a web page on lightning. I've done a lot of research on it and how it affects things. Lightning can seem quirky, but it behaves quite normally for a semi-random multi-frequency pulsing RF current at high voltage.

Lighting doesn't "see" the ground as a solid object. The large electron clouds and positive charged areas seek ways that they can connect and equalize charges. Sandy soils that are relatively dry don't act as good conductors, nor is any earth a consistant conductor. (Sea water, OTOH, is an even conductor.)

A phone line buried in the ground isn't really protected from lightning, since bolts of lighting will actually burrow through the ground to get to an area containing a charge. One result of this and proof of the effect is a fused tube of dirt and sand called a fulgurite.

True protection from power line and phone line surges requires a single point bonded ground system at the main electrical, phone, and cable tv entrance, and surge protection at that point. The ground has to meet specifications that many home ground systems do not attain.

Using small UPS units or surge protectors can actually create problems if not properly handled. Example: Your computer is on a UPS and you think it totally protects the computer. The instructions on the UPS say not to plug a laser printer into the UPS and it only has two sockets anyway, one for the computer and one for the monitor. You plug the laser printer into a wall socket or cheapie surge protector.

When a big surge occurs, the cheapie surge protector blows the MOV inside, leaving you with no protection on the laser printer. The next surge finds a path through the laser printer, through the printer cable, and into your computer.

Network cards are designed with some surge protection, and the coils in a modem choke out some surge before they self destruct, but any large surge or near strike can take out equipment.

Even if the equipment isn't destroyed otright, and seems to work afterword, the components have often been stressed by the overvoltage and some may fail within a short period of time or operate outside of normal values, which can lead to a computer acting "funky" but seeming to work most of the time.

There are lightning prevention systems and lighting protection systems available, but the installer has to know exactly what he is doing and why to make them effective. Lighting can use such things as linoleum as a conductor, and can refuse to make sharp turns on a large conductor, preferring instead to arc to a more straight-line path and smaller conductor. This "no sharp turns" effect has given rise to the highly questionable practice of tying "choke" knots in power cords as a method of surge suppression. The idea has merit when a toroidal coil is designed to tune out surges, but knotting a power cord is an unreliable method of protection.

The simplest and most reliable protection for electronic equipment during a storm is to unplug it from all external wires. Short of that, computers and equipment should be powered by a single source that is properly grounded, and kept in a very tight configuration, where no ground loops can occur. A surge strip can be more helpful as a single plug to unplug than as a protected power source.

The area where I live has incredible storms. A few years ago conditions were right, and there were storms where there were literally as many as ten lightning strikes in the immediate area per minute, for periods up to twenty minutes at a time. At least once or twice a summer we are treated to a light show of "boiling" lightning, where a distant storm or two will have clouds nearly constantly lit by lightning. Watching two distinct and seperate storms, I've seen them interact electrically where a discharge in one storm will be followed by a discharge in the other a few seconds later.

Lightning in Florida is better than most movies.


 


Posted by William Hooper (Member # 71) on 07-12-2001, 01:35 AM:
 
quote:
The funny thing is, none of the 'phone lines are carried on overhead pilons in my neighbourhood - they're all underground. So I've no idea how the lightning got into the system.


Much major damage from lightning is from induced voltages, not direct "connection" to the lightning. Paul has probably seen all the humorous aerial photos of AM radio tower sites after a lightning storm where the induced voltages in the underground radials draw fried brown designs in the earth.

One of the main reasons that almost all network cabling now is twisted pair instead of coax is that twisted pair is less prone to induced voltages.

Leo's right about phone lines, though. If it gets into the phone lines (yes, they're usually twisted pair, but it happens) & then to a computer or automation interface, off it goes as a direct strike through the network, any audio, & AC lines. Phone lines need serious isolation & lightning protection.

This topic is in the Ground Level forum!
BWA-Ha-Ha-Ha!

Okay, joke's over.



 


Posted by Brad Miller (Member # 2) on 07-12-2001, 04:16 AM:
 
Well, the original post of this thread DID inquire about booth policies AND floor policies during power outages. Sometimes things wander.
 
Posted by Jerry Chase (Member # 660) on 07-12-2001, 09:05 AM:
 
"Much major damage from lightning is from induced voltages, not direct "connection" to the lightning. "

William, I argued this for quite a while, but was eventually shown it just isn't technically correct. Damage occurs from ground loops where there is a voltage differential, and from direct hit on a line and resultant surge, and from slower discharges that don't always generate a lightning bolt, but very rarely from voltages caused by induction. The short time span involved and the "de-tuned" nature of the beast dictates that very little induction occurs except in very rare cases, and the amperage of the induction is usually insignificant. The only semi-documented case of damage by induction I could find was a report of a high-tech x-ray machine that had been damaged even though it was totally unplugged. Even here, there was a question whether a charge had propagated across the surface of the floor.

What does occur is an entire area will become charged and parts of the area where ground leaders occur may have a greater potential than adjacent areas. Even though a "failed" ground leader isn't the primary discharge path, it can still be discharging some local currents. A leader doesn't even have to glow to exist and be moving electricity, and I *suspect* a full blown lightning strike may not have to occur to damage particularly sensitive equipment. A lot of what gets described as "induced current" damage is much more likely damage from secondary or failed leaders.

Bringing it back closer to topic, most newer theatres are protected from effects like this by the metal roof decking and drier air in the building. Charges go up the rebar or gutters and bypass the interior spaces.

Burn marks around radials can occur for a number of reasons. My dad was C.E. for an A.M. station with 3 free-standing 500 ft sticks. The towers were regularly discharging during storms as well as getting hit. The spark gaps between the paired volleyball sized electrodes would light up the ground at night, making them clearly visible from the transmitter building. The radials collected (or dissipated depending on your preference of terminology) all that energy.


 


Posted by Dustin Mitchell (Member # 372) on 07-13-2001, 12:25 AM:
 
Getting back on topic ...

Your first priority, as John P. pointed out, is audience safety. Following is the list of things, in order, of what I would do/have done in the case of a power outage:

1) Instruct your projectionists to follow your set emergency procedures (you do have one, don't you?). This should include shuting down breakers, etc as has been noted in this thread. You can also have them check to make sure none of the electrical panels got shut down accidently thus causing the outage (a good thing to do before you get to involved in taking care of the situation). The projectionists should be responsible for shutting down all breakers in the building, not just the ones in the booth. Your ushers will have enough to do without worrying about that.

2) Your ushers should handle the patrons, assign concession people to help if nescessary. One person should be posted in each corridor, informing patrons who are spilling out to please remain in their seats while theatre management contacts the power company about the temporary power outage. Make sure the employees inform the customers that the power could come back on at any time, and when it does their movies will start exactly where they left off. While these employees watch each corridor, send the remaining ushers to each auditorium where they will make a similar announcement.

3) Make sure your cashiers are informing people similarily, that the outage may only last a few minutes and as soon as the power is back on they can purchase tickets.

4) You, as the manager, will have to make two very important phone calls. Remember that your phone systems central panel runs on electricity, so it won't work. You'll have use the payphone in your theatre. If your theatre doesn't have a payphone, get one! But in the meantime, you'll have to go somewhere that does have one or a regular phone you can use. First call the power company and infrom them of the outage (they don't automaticaly know, you have to call and tell them). Then call your District Manager or City Manager, whoever it is who is directly above you. Inform them of the situation and the steps you've taken. This isn't meant to be a sign of weakness/call for help, it just informing your superior of a situation they should be aware of. Usually they'll say fine or "keep me informed." If they do, you know your doing your job ok so far.

Now it becomes a wait and see game. What the power company tells you (if you talk to a real person that is) will determine where you go from here. While you are waiting, remember your concession stand can still be open (that is if the cash drawers aren't locked until a sale is rung up). You won't be able to sell pop, but you can sell the popcorn remaining in the bin, candy, nachos (as long as the cheese stays warm), bottled water, pretzels (as long as they stay warm), etc. Just have your concession attendants record all sales on a piece of paper in their drawer so they can be rung up after the power comes back on.

Security will be an important issue, since your security cameras wont' be working. If you think its nescessary, post a guard at the office door to watch over the safe. Take all box office drawers to the safe, you won't need them until the power comes back on anyway.

Do not keep your patrons waiting in the auditoriums anymore than half an hour. Not only will they get irritated, but safety becomes an issue. Emergency lights don't last forever. You DO NOT want patrons still in the theatre when the emergency lights start going out. After half an hour or less (your descretion), have your ushers make the rounds of the theatres again, this time giveing the "We are very sorry..." speech. Tell the patrons that their tickets stubs (which should have the date and time on them) will be their rainchecks, and will get them into any show, any time afterwards. You may wish to put a time limit on this, say two or three months. If your theatre is really full, you may want to stager the auditorium announcements, but remember, time is off the essence, get them out before the lights go out! Now this part is very important, DO NOT GIVE CASH REFUNDS UNLESS IT IS ABSOLUTELY NESCESSARY! Some people may disagree with me here, but this is a business, and giving out $4,000 in cash after an outage just doesn't make any sense. If someone is adament about getting their money back, return the dough discreetly, out of view of the other customers to prevent a mad rush to get their money back.

Now that your patrons have exited (if they did), your going to have to do something about the film. If you wait until the next set to rewind it, your going to lose a whole set of shows, you can't very well sell tickets to movies that are half over (if this is the case). If a movie is only in the previews, or even half way through the first reel, you can probably cut it and drop it back in the roll. I wouldn't attempt this if the movie is more than halfway through the first reel though. The following procedure is for the movies more than halfway through the first reel. It is risky and should only be attempted if you are confortable around film. Get together your projectionists, managers (leaving one to watch over the floor), and any ushers you think are responsible enough to handle this. Make sure each print is suction cupped/beaven pooed down securely. Unload the projection, leaving the film on all rollers except the lower magazine roller. It should look like your about to thread buttom up. Now, making sure the film is securely in place, spin the platters through by hand. You can probably do two or three at once, making sure the film is on all rollers, etc so it does not get damaged. You should be able to spin the film through at two to four times speed without any danger of damage. Some here may disagree with this, but it beats running your movies through to empty screens just to rewind them. I've had to do it several times, and have never had any problems.

Once your film has been rewound and the patrons exited, your job becomes boring again. You have to wait around until the power comes back on. At some point, your going to have to make a decision of whether or not to just close for the day. This decision should only be made after speaking with the power company and your immediate superior. Have your staff clean up as best they can, keeping in mind there won't be any water pressure and probably no lights. You'll have to come in later on when the powers comes back on to close out the computer, ring up the concessions sold during the outage, punch out employees, etc.

Basicaly, dealing with a power outage involves having set procedures and keeping a cool head.
 


Posted by John T. Hendrickson, Jr (Member # 849) on 07-13-2001, 06:57 AM:
 
Dustin:

Thanks for your lengthy post and taking the time to respond. Terriffic! You covered a lot of ground (no pun intended) and this was what I had hoped would come out of this thread.

Many of our procedures are similar, but there are some additional things you mentioned that we can definitely use.

I agree that projectionists should shut down breakers in the booths, but in our situation they would be unable to get all the breakers downstairs due to the fact that we have a number of pannels spread over a wide area, so we assign that aspect to the head usher.

We feel cash refunds are big trouble in these situations, so we offer unrestricted passes, no exceptions.

Anybody else out there who has something to add?
 


Posted by Steve Scott (Member # 630) on 07-15-2001, 10:45 PM:
 
If accidental power outages weren't a problem, my staff shutting off the wrong breakers at night (The silent alarm, lobby lighting, hand dryers in the bathrooms) is what I'm still trying to manage.

I remember when it just took a strip of masking tape with arrows next to the right breakers to get the place shut down. Now, we had to (finally) install stoppers on the breakers that have to be left on!

Thank the film gods that the projection booth breakers are off limits to the regular staff!!
 


Posted by Ron Keillor (Member # 1790) on 08-16-2003, 03:30 AM:
 
Topic from a couple of years ago could use a timely bump.
What I didn't see was a note to ensure refigerators and freezers were shut to protect perishable confection stock.
 
Posted by Jack Ondracek (Member # 1466) on 08-16-2003, 11:03 AM:
 
Now that drive-in sound is mainly on FM, computer-type battery backups can keep your sound system up long enough to let the crowd know what's going on. They all have headlights, so the concession building interior is probably the only concern there.

On the other hand, the increased attention drive-ins have enjoyed in recent years has brought this issue "to light", as it were. The idea of sending an entire house out of the place can be a PR nightmare. One single incident... 1,800 bad impressions, multiplied by all the subsequent conversations. Of course, the outage occurred just after you started, so everyone wants their money back... which means they all have the ones & fives, and you have a bucketload of 20s & etc!

Truly a "scary movie". Last year, I had a manual generator transfer switch installed at my mains panel, and put one of those big shore power sockets on the outside wall. I got a used 3-phase diesel generator & put a (big) cord & plug on it. It takes about 10-15 minutes to tow the generator to the building, plug it in, start it up & switch the load to it.

We may not need it often, but Murphy's Law out here holds that a squirrel will blast one of your high-side fuses on a sold-out Friday or Saturday, and you might not even know it until you try to start the show. Preventing the bad PR & lost income from one or two of those events would cover the cost of the equipment.
 
Posted by Ken Layton (Member # 133) on 08-16-2003, 11:46 AM:
 
Jack's right. That generator of his will run just about the entire drive-in except for the pizza ovens.
 
Posted by Dave Ganoe (Member # 53) on 08-16-2003, 02:41 PM:
 
We use cp650's at our location and when you get the power pulse from a storm or something sometimes they do switch to non sync and the film keeps running. With 10 screens spread out over 4 floors its tough to get to them in a timely manner. Got the ok to purchase ups to take care of those momentary interruptions and hopefully cut down on customer complaints.
 
Posted by Sean McKinnon (Member # 612) on 08-17-2003, 11:19 PM:
 
All I have to add is that there is nothing much like carrying 300 pounds of dry ice up two flights of escalators to a walk-in freezer when your complex blows a transformer!
 
Posted by Ky Boyd (Member # 23) on 09-03-2003, 02:27 AM:
 
Sean, Ok, I'll bite. What does your theatre do with 300 lbs of dry ice???

One aspect I didn't see mentioned in the thread but I may have over-looked it, is having working flashlights available to the staff. Batteries should be checked regularly. Have enough extra batteries on hand for every flashlight. Check periodically (monthly or more often) that every area that needs a flash light has one. The darn things seem to grow legs and wander, most frequently to the booth! We have a flash light by every projector (our booth is a bit spread out) as well as several downstairs in the concessions and box areas and the usher closet.

With regard to ticket stubs as rainchecks - my personal preference is to issue canceled show passes (aka shit happens passes) rather than keeping a list of acceptable old tickets in the box office.

Don't recall if anyone mentioned locking the front doors, but that too is typically pretty standard operating proceedure so that no one gets in until the power is restored but people can leave.
 
Posted by Lance C. McFetridge (Member # 95) on 09-03-2003, 06:07 AM:
 
Ky,
Do you have your RTS Software print a cancelled show pass, or is this something you have on hand?
lance
 
Posted by Mike Williams (Member # 1140) on 09-03-2003, 08:34 AM:
 
You can print a cancelled show pass? If the power is out that might be difficult [Mad] (especially on a busy night).
 
Posted by Jack Ondracek (Member # 1466) on 09-03-2003, 12:01 PM:
 
We did our "annual load test" on Monday, as it was our first day off for the fall season. As the generator is trailered, it's not convenient to throw a load on it whenever I start it up (about once monthly during the season). We run up the whole booth, field lights & all, both shows, and kick on as much of the concessions as it will take.

Other than not being able to run the air conditioning (awwwwww...), it handled the place nicely.

We're looking forward to converting the grill & pizza ovens to propane next year. That should give us all the extra headroom we'd need.
 